    Ground to Neutral?
    Intro: I rehab homes for a living and tent to get older homes that I don't always gut down to the frame therefor I don't always have the option to update the old 2 wire (without ground wire) electrical system to a 3 wire (with ground wire). My problem is I want these homes to have 3 prong outlets so that the people that buy them can plug in there computer and like items.

    Now if the neutral is grounded at the panel then why is it wrong to take a short ground wire from the ground on a outlet to the neutral wire on the outlet. My thought is if the neutral is grounded then what is the need to have one wire dedicated to ground for each circuit and one for neutral if they are both the grounded.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jan 23, 2012, 07:05 PM
    Where are you working? I do similar work and the permits frequently force me to upgrade all electrical including the panels, maybe I am mising a loophole. You can install GFCI receptacle and this would allow 3 prong plugs, still not grounded but now GFCI. BTW, I am also required to upgarde bedrooms to Arc faults too
    UsaveU's Avatar
    UsaveU Posts: 25, Reputation: 1
    New Member
     
    #3

    Jan 23, 2012, 07:32 PM
    I work in Ohio, but I am not pulling permits for small things like this. I am worried about it causing problems down the road for the new home owner. I know a home inspectors outlet tester will show that the plug is grounded if I wire it like I stated above but I don't know if there is a reason not to wire it like that.

    Note: I do pull permits for whole house rewiring or breaker panel updates. ( do not use lienced electricians because I pull the permits)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 23, 2012, 07:44 PM
    The fact that they connect to the same place in the panel makes no difference whatsoever.
    The ground is supposed to carry only fault current. The neutral carries circuit current.
    If the ground and neutral are connected outside the main panel, and there is a problem on the neutral of the circuit, the ground and all bare metal associated with the circuit can and will be live with voltage.

    Your logic is an old and weary one. This argument/question comes up all the time. Just take it as fact that jumping out the ground to neutral (called a bootleg ground) is a bad and potentially dangerous thing.
    Sometimes "small" things like this might not be so small.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No ground bus... Do I hook ground to neutral? [ 2 Answers ]

If my older home does not have a ground bus, should I connect the ground of a new run to the neutral bus? If I connect the ground to the neutral bus, should I add a grounding rod and connect it to the neutral bus? There is no room in the panel to add a neutral bus, and no room to replace the whole...

Voltage between the ground and neutral [ 2 Answers ]

I am getting a reading of 50 volts between ground and neutral, and ground and hot. In the j-box where the 12-2 romex is connected to the hot and neutral. I disconnected the ground wire in the romex completely. The ground is not touching the j-box or anything else. On the other end of the same romex...

Neutral / Ground [ 3 Answers ]

OK Strat, Here is the photo clip of the schematic of the Neutral /Grounding system in my place. Don

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...

Using Neutral as a Ground ? [ 3 Answers ]

In my new apartment there are some wall outlets that are two prong outlets. Also my fear is that the three prong outlets are not “physically” connected to ground. I heard somewhere that in this kind of system the neutral wire can also be used as a ground. Is this correct? Would a separate...


View more questions Search