    I have a 20 ye old heil nguk direct vent furnace. It has electronic spark. The inducer comes on when stat calls for heat but nothing else happens no gas relay l
    Ignition or flame just continuous running of inducer flame sensor ignitor replace as well as the spark wire and relay
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #2

    Jan 20, 2012, 07:32 PM
    Start by using a multimeter to see if the pressure switch is closing after the inducer motor spools up to speed. When the inducer motor is energized you should see about 24 VAC at one side of the pressure switch and if it closes, see that voltage on both sides of the pressure switch.

    Report back what you find.
    Fitzgoblin's Avatar
    Fitzgoblin Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 20, 2012, 07:32 PM
    Heil furnace
    Inducer comes on in 20 year old HEIL nothing else happens no intermittent spark or gas relay help
    Fitzgoblin's Avatar
    Fitzgoblin Posts: 3, Reputation: 1
    New Member
     
    #4

    Jan 20, 2012, 07:35 PM
    Hi seatttle pioneer I've bought parts from you before with great success the pressure switch is fine there doesn't seem to be incoming voltage to control module
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #5

    Jan 20, 2012, 08:06 PM
    Hmmm. You are sure you are not getting any 24 VAC voltage to the pressure switch? Please explain in detail how you are checking that. You should have the inducer motor running while testing.

    Check the voltage at the R and W terminals as well and tell me what you get.



    I did sell parts on Ebay a year ago--- did you buy parts from me there?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire my greentek hrv to kicks on the furnace fan on low of a heil furnace? [ 0 Answers ]

How to wire my greentek hrv to kicks on the furnace fan on low of a heil furnace? I had a airconditioner installed in August and for some reason they unhook my hrv so now the hrv turns on but doesn't request the furnace fan to come on. So now it's not circulating the air in my house properly. I...

I have a heil 9000 furnace I turn the furnace on and nothing happens [ 0 Answers ]

I hear a hissing noise coming from the inducer motor and the pilot does not come on what can the issue be

Heil furnace problem [ 0 Answers ]

I got a furnace that's about 10 yrs old , smart valve was bad so replaced it,after powering it up everything works fine until I put the outside cover back on and it stops working, thought might not have enough line pressure coming in, checked and its OK. Take cover back off and furnace works fine....

Heil Furnace-Combustion fan comes on but furnace does not come on [ 12 Answers ]

I have a 10 year old Heil furnace. When the furnace tries to come on the combustion fan comes on but nothing happens after that. The pilot does not come on, no flames, nothing. I hired a service tech and he said that we need to change the gas valve since it faulty. Is there anything else I...


View more questions Search