    Gas valve closing
    Ihave a luxaire 90 gas furnace the inducer starts pressure swithch closes, hot surface ignitor glows burners ignite once the hot surface ignitor shuts down the gas valve closes, the thermacouple is working just installed a new one and I jumped out the rollout safety. Any ideas?
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #2

    Jan 20, 2012, 06:55 PM
    Hot surface ignition furnaces don't have thermocouples. Did you replace the flame sensor?

    Describe in more detail what happens when the HSI heats up and the gas turns on.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    Jan 20, 2012, 06:57 PM
    You should have a flashing light on the control board giving you the fault code. You need a good equipment ground on the gas valve and control board for the flame sensor to work and sense the flame. If it's a pressure switch fault you need to make sure you have a clear exhaust and intake pipe. A restricted condensate drain will open the pressure switch also. Good luck I hope this was of some help.
    mcosta's Avatar
    mcosta Posts: 2, Reputation: 1
    New Member
     
    #4

    Jan 20, 2012, 07:09 PM
    Yes I am sorry I replaced the flame sensor and also jumoed out the roll out switch. The HSI lights up opens the gas valve and lights the burner but it seems that when the HSI shuts off the gas valve then closes putting the burners out tries that 3 time then goes on lock out I have 7 flashes on the led board
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #5

    Jan 20, 2012, 07:17 PM
    It should say on the door of the furnace what fault code 7 is. If you can locate it. It will help expedite trouble shooting.
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #6

    Jan 20, 2012, 07:40 PM
    How long do the burners stay lit before shutting off?

    Finding the diagnostic code for the seven flash will probably confirm that the furnace is shutting off because the burner flame ignition isn't being detected.

    Check to be sure that the wire from the flame sensor is properly connected to the circuit board and that the circuit board has a GOOD ground connection.

    Also, measure the AC voltage between the flame sensor wire and chassis ground while the inducer motor is running and report that voltage here.

    You may have a bad circuit board that is failing to detect the burner flames.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Zone valve continuously opening and closing [ 2 Answers ]

The zone valve to one of my buildings is constantly opening and closing. Within minutes. I checked the sensor on another building and it is working fine. I don't know if the valve is not getting a signal, maybe a wire is loose (although I have followed them and don't see evidence of this). Is...

Heil Gas Fur smart valve sv9541 cycles, clicks valve, lights pilot on off.Flame? [ 1 Answers ]

I have a Heil Natural Gas Furnace with smart valve sv9541 that goes off and the valve click as the ignitor glows on and off while lighting the pilot light which then goes out, and back lit?Is this a flame sensor problem? Thanks for advice.

Can I replace gas valve with universal valve? [ 3 Answers ]

I have an older Carrier natural gas furnace (1970s). Pilot doesn't stay lit. New thermocouple didn't help. Repair man says I need a new gas valve, $700 plus install, suggests replace entire furnace. Can I replace valve with universal valve and save $$?

"gurgle' from heart valve not closing tightly [ 2 Answers ]

I was recently diagnosed with this problem. My doctor says a lot of women get it. Anyway, I don't like the sound of it. I won't see my doctor until 9/17. I may be a wreck by then. Has anyone else experienced this? Did you have any symptoms prior to your diagnosis? /FONT] Thank you for any light...

Gas valve noise on main valve engagement [ 1 Answers ]

I have a carrier 58gs100ga furnace with a white rodgers 36e93 gas valve. The main gas valve solenoid chatters or rattles for a split second before it stays engaged after the pilot is proved. I just replace the spark/lock out board and the fan board for a different problem. This chatter is...


View more questions Search