    Wiring a four gang box
    Bathroom fan/light replace & wall removed in bathroom remodeling project. Using 12/3 for bathroom fan / light, 12/2 for shower light, 12/2 for outlet. All wires feed to four gang box being feed by 12/2 wire on 20 amp service lead. Question is connecting black to switches. My understanding is to pig tail off hot to each switch inturned switch is connected to load. Could I use a push in jumper at each switch instead of separate pig tail off black?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jan 20, 2012, 08:48 AM
    There are numerous codes you need to be aware of before starting this project.

    #1 - The you must use a GFCI receptacle or a GFCI breaker. You can use a single 20 amp circuit fr the entire bathroom, but that does make it critical that you place the GFCI receptacle in the correct position otherwise, you may end up with the Lady of the home standing in a dark bathroom holding a hair dryer and saying unkind things about you. :)

    It would be wiser that you run a dedicated 20 amp circuit for the GFCI receptacle (as required by code) and a second 15 amp circuit for the remainder of the devices.

    This way if the GFCI trips, the lights are still on.
    cdrn48's Avatar
    cdrn48 Posts: 5, Reputation: 1
    New Member
     
    #3

    Jan 21, 2012, 04:26 AM
    The existing circuit (#2) I am working off serves the tub/shower & toilet area and is not a GFCI circuit. There is an exsiting, separate, 20 amp circuit (#1) for the sink area which is GFCI protected. I plan to relocate #2 circuit to a GFCI outlet then to the gang box. Am I correct in that is should have separate pig tail off the hot lead (black)to each switch? Then connect all common (white) together. Ground will also be pig tailed to each switch. Any suggestions for connecting any of these wires would be greatly appreciated. Thanks.

    Cdr
    cdrn48's Avatar
    cdrn48 Posts: 5, Reputation: 1
    New Member
     
    #4

    Jan 21, 2012, 04:38 AM
    I am working on a separate 20 amp circuit which serves the toilet & shower area; labeled as (#2) circuit, which is not GFIC protected. My (#1) circuit is a separet 20 amp GFIC protected circuit, severing the sink area. Original lead for circuit (#2)is 12/2. I would like to relocate (#2) circuit to an exsiting GFIC outlet then connect my four gang box with fan/light on 12/3, shower light on 14/2 and additional GFIC outlet on 12/2. what I am not clear on is tieing my wires together. Should I tie all common - white - together, then pig tail off the ground to each switch and pig tail off each hot - black - to each switch? Any feed back or suggestions would be greatley appreciated. Thanks.

    Cdr
    cdrn48's Avatar
    cdrn48 Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 21, 2012, 05:56 AM
    Follow up to wiring four gang box
    I am working on a separate 20 amp circuit which serves the toilet & shower area; labeled as (#2) circuit, which is not GFIC protected. My (#1) circuit is a separet 20 amp GFIC protected circuit, severing the sink area. Original lead for circuit (#2)is 12/2. I would like to relocate (#2) circuit to an exsiting GFIC outlet then connect my four gang box with fan/light on 12/3, shower light on 14/2 and additional GFIC outlet on 12/2. What I am not clear on is tieing my wires together. Should I tie all common - white - together, then pig tail off the ground to each switch and pig tail off each hot - black - to each switch? Any feed back or suggestions would be greatley appreciated. Thanks.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jan 21, 2012, 06:19 AM
    Please keep related posts in the same thread.
    cdrn48's Avatar
    cdrn48 Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 21, 2012, 02:24 PM
    Did not know how to reply

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Diagram on wiring 3 lights & 1 outlet in 1 3 switch gang box? [ 1 Answers ]

You provided a diagram of 1 gang box controlling 3 lights and 1 outlet before. I can't seem to locate it. Can you please Master of all Electricians please provide another? One of many who appreciates your knowledge, Sonia galicia Email: [email protected]

Can two circuits share the same gang box [ 2 Answers ]

Is it code for a 220v switch and a 110v outlet to share the same gang box? They are two different circuits going to the same outdoor gang box?

To pigtail or not to pigtail -- wiring double gang box [ 4 Answers ]

I would like to wire a double gang box with two pair of receptacles on the same circuit and not switched. Technique 1: One source told me it is preferable to pigtail hots, neutrals, and grounds to each receptacle in the box so that a possible future receptacle replacement might be easier. ...

3 Gang Box.not a clue [ 3 Answers ]

Hello all... New York City here. I have to use BX... code. I have 2-wire( there is no ground in BX by the way in 2-wire) ran from the breaker. It is for my bathroom. The house was built in 1938 or 1939. The entire top floor (2 bedrooms and 1 bath) is all run on ONE breaker!! That is how...

5 gang switch box [ 7 Answers ]

I have a 5 gang metal switch box with 5 switches. I want to eliminate one of the switches so I have only 4 switches. I don't want to use a blank to fill the hole with no switch. I want to use a switch plate for 4 switches. Can I cover the hole with a metal plate and mud over it so it looks like a 4...


View more questions Search