    Nov 26, 2011, 04:16 PM
    I have a parking lot light that's 480 can I run it on 120
    Can anyone help me convert a 480 light fixture to work on 120
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Nov 26, 2011, 05:56 PM
    Are you planning on changing out the fixture and the bulb with a unit that will operate on 120?
    dnsent's Avatar
    dnsent Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 26, 2011, 09:34 PM
    I was hoping not to I just didn't know if there was a way to make the unit run on 120 can the transformer be stepped down to run on 120?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 27, 2011, 05:36 AM
    You can get a transformer rated 120 volt/480 volts, need to size the VA 25% higher than the input watts of lamp and ballast combination.

    For example, a 400 watt metal halide fixture will have an input of 450 watts plus 25% will require a transformer rated at least 600 watts (VA).
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Nov 27, 2011, 06:11 AM
    And by the time you buy and wire the transformer you could have either replaced the ballast kit in the fixture or replaced the whole fixture itself, for less cost and less work.

    It is a rare case where making a 480V HID fixture work at 120v is worth doing.

    Are you sure the fixture is not multi-tap?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

On a 480/120, 208 transformer is a main needed on the 480v. Side? [ 2 Answers ]

Is a main disconnecting means needed on the primarary side of a 480v transformer with a 120/208v secondary if the transformer is 150' away from the MCC?

Advantages of a 480/277 3 phase Volt system over a 120/240 [ 2 Answers ]

I have customer that needs to upgrade his service from 800Amps to 1200Amps. He currently has a 120/240V 3 phase system and a 120/240V System With 2 separate Meters. I am advising that he upgrade and go to a 1200Amp 480V 3 phase system and transform down for existing loads. Will he save any costs on...

277/480 load after transformer = to 120/208 load feed [ 1 Answers ]

I have a 800 amp 120/208 3P stand up section that feeds a step up 90kva transformer and the loads are nearly equal? I thought that after the transformer the load of 277/480 would be drawing less. We have about 500 amps per phase being drawn in front of the transformer and the load at the sub...

Wiring a parking lot light to breaker box with a timer [ 1 Answers ]

Hi every one could use help I have a parking lot light and timer box I need to wire up to breaker box any help would be aprreiated


View more questions Search