    54vac on gnd, 71 on hot, 0 on neut
    Ok, so I have suddenly realized I have a electrical problem in my new house. I am an aircraft electrician with quite a few years of experience, however, don't deal in control circuits often.

    So, On one circuit - 4 outlets, including an outlet in family room, and can lighting in kitchen all have 54vac on the ground wire. The neutral has 0 on it. Hot has 74 or so. I checked these all with a run of wire to my water pipe to ensure I had a good ground. I've pulled out all the outlets in the basement to look for loose connections or grounds touching -- nada. I'm assuming my next step is to crawl into my attic and check the can lighting. I can isolate everything one at a time if I have to, but I'd like to know if there's anything Im overlooking.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 26, 2011, 12:51 PM
    Let me ask this in a different way.

    When you measure between Neutral and Hot, you get 74 VAC?

    When you measure between Ground and Hot, you get 54VAC?

    Or are you using the cold water pipe as the ground leg? Is the cold water pipe bonded to the Main Panel Board?

    If you are (for illustration only) in a bathroom and using the cold water pipe you need to make sure that there is 0 (Zero) resistance between where you are and the main panelboard.

    Some times, a plumber will slip a PVC filling and thereby destroy the 0(Zero) ground reference point.
    Kokuathu's Avatar
    Kokuathu Posts: 9, Reputation: 4
    New Member
     
    #3

    Nov 26, 2011, 01:23 PM
    Neutral - hot 120vac
    Ground - neutral 54vac
    Ground - hot 64vac

    The water pipe I am using in my basement to test bonded to gnd, 0.0 to gnd on the panel.

    So when I test using that ground as my reference, I have 54vac on gnd, 0vac on neutral, and 64vac on hot
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 27, 2011, 05:32 AM
    Sounds like a neutral to ground short. Start at the beginning of the circuit where you can find 120 volt to neutral, and zero neutral to ground. Take each segment of circuit apart, and begin connecting each at the beginning and checking at the end of each segment.

    Since you have already checked each outlet and junction box, perhaps there is defective section of cable, either by a nail/screw or mice.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theoretically what happpens when a receptacle wired hot/neut reversed? [ 1 Answers ]

What happens theoretically to a receptacle when the hot and neut wires are hooked up to the reverse screws? This is a question about the anatamy of a non GFCI receptacle. Besides the difference in the screw, is the device symmetrical? If it is symmetrical it would seem to make little...

Gnd buss [ 2 Answers ]

I need to know the awg for a hot wire neutral wire &

Gnd Buss Clarification [ 1 Answers ]

I putting in a 100amp sub panel. I know you have to keep the neutral and ground separate in the sub panel. BUT there are two neutral bars one on each side in my GE box. My question is can I take the bar out that connects the neutral bars together, use one for equipment grounding and the other for...

Gnd @ Main Panel [ 4 Answers ]

Ok.. I posted on this before but I can't find it on the board. I want to know about installing my ground at my svc panel. I am running out of this to a small shop to a 100amp sub. I understand about the gnd and neutrals being separated and such at the sub etc. What I am wondering is this: As...

6/3 w gnd. [ 2 Answers ]

Ran into conflicting answers locally on this one. Can you bury 6/3 , in conduit if it is NOT rated for burial (inside use)? Or any wire for that matter (12-2,14-2 etc.. )Some around here seem to think so. Some do not. I say NO, but I'm not an expert on this subject.


View more questions Search