    I'm installing 3 baseboard heaters rated at 120 volt, 1500 watts.
    Can I connect 3 baseboard heaters rated at 120 v and 1500 watts to 1 t-stat to control all of them?
    What size wire and breakers do I have to use? And shoud the t-stat be single pole or double pole.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 20, 2011, 12:38 PM
    Each 120 volt 1500 watt heater needs it's own separate 15 Amp circuit with #14 -2 plus ground cable and a 15 amp circuit breaker.

    Each circuit will needs it's own single pole t'stat.

    If you absolutely need to have one t'stat, it gets more complicated that the t'stat needs 120 V control voltage to operate a 3 pole contactor that would then operate the three heaters.

    If you have limited experience, apparent by this question, you may need a professional to install a contactor system.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installing baseboard heaters [ 3 Answers ]

I am installing electric baseboard heaters in 3 bedrooms and they are 240 volts and a have 3 slots in the panel to install the breakers. When I went to purchase them I was told that a single pole 20 amp breaker would work, however all that I have been reading is telling me that I need to install...

How many minutes will a 44 watts 120 volt 21" TV [ 1 Answers ]

I have rv with 4 deep cycle batteries

What is difrence between 120 volt rated breaker and 220volt? [ 2 Answers ]

Can we use 400/230 volt rated breaker in 208/120 v system?

What's the difference between a 120 volt and 120/208 volt system? [ 2 Answers ]

We offer our unit in a 120 or 277 volt version. A customer just told me he is using a "120/208" system. What does that mean and will our 120 volt rated product work with it?

Wiring 120 volt, 1250 baseboard heater [ 5 Answers ]

House has a 120 volt, q-mark hyd electric baseboard heater ran on 14/2 cable with 2 recepticales of the same feed. 15 amp breaker in panel. Is the OK? Thx


View more questions Search