Wire sizing and conduit sizing
[ 8 Answers ]
I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...
5 HP 3 P wire and CB sizing
[ 3 Answers ]
I have a 5 HP, 3 ph DOL started motor driving an air blower. The motor is situated at approx 50 mtrs from the nearest DB . Could you tell me the cable size and nos, type, rating, breaking capacity and the locations of MCBs in the motor circuit starting from the DB? <moved from Electrical...
Wire Sizing
[ 2 Answers ]
I am rewiring a house in Mexico and following the 2002 NEC for wire sizing, grounding, circuits, etc for all work from the meter on. Service panel is 125A and will support air condition along with all other lighting and appliances. The utility company will only supply a 6 AWG overhead triplex...
Sizing Wire
[ 3 Answers ]
Im running a new 100amp sub about 40 ft from house. Ive been reading but wanted to know you guys' opinion. Should I go with THWN #3 for my Hots/Neutrals. And #8 for EQ Gnd.? I'm kind of confused about the 90/75 degrees that rate this type wire. Also I understand about having to conduit... View more questions Search
|