    Water pressure relief valve leaking?
    As I was leaving this morning, I noticed the cold water relief valve leaking outside my house. My washing machine was running. I flipped the relief valve a few times to see if perhaps it had some debris keeping it open, but it didn't shut off entirely. The relief valve is located on the OTHER side of the cold water pressure regulator.

    Any suggestions or concerns are appreciated! Best, Herb Katz
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Nov 7, 2011, 06:29 PM
    You are using terms that aren't quit right. Is this a relief valve or a pressure reducing valve?
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #3

    Nov 7, 2011, 06:59 PM
    Measure pressure on the inside of the house. If you measure more than 75 lbs than your pressure regulator needs to be rebuilt or replaced. The pressure relieve valve leaks when pressure approaches 150 psi. I suggest after you replace pressure regulator to replace pressure relieve valve as well. Back to you. Milo
    HerbKatz's Avatar
    HerbKatz Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 8, 2011, 06:23 PM
    Thank you!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Surging water pressure & leaking water heater relief valve [ 19 Answers ]

Just recently the pressure of our water in the house surges when we turn a faucet on, and the city water company verified that our pressure in the house when we open a faucet is higher than the pressure in the lines in the street, and after the water runs is at a normal pressure (meaning their...

Cold water pressure relief valve leaking [ 6 Answers ]

My pressure relief valve is leaking. This is a very small amount of water dripping to the outside of the house. Next to replacing the valve is there anyway to stop the leak. This valve is within 2 feet of the pressure regulator where the water comes into the crawl space.

Cold water pressure relief valve leaking, not the TRP valve [ 5 Answers ]

Hello. Cold water pressure relief valve start to drip water through the drain pipe. I replaced it with a new one but it is also dripping water. I have reduced water pressure in the house to the minimum by turning main water supply valve but it still leaking. Thanks for your help.

Leaking pressure relief valve on h/w tank [ 4 Answers ]

The pressure relief valve keeps leaking. The h/w tank is about 9 months old. The problem started when the main line broke. The township had to turn my water off and when they fixed it and turned the water back on is when it started. Any help towards a solution is always appreciated. :)

Gas Hot Water Heater Pressure Relief Valve Leaking [ 6 Answers ]

Should the pressure relief valve on my natural gas hot water heater leak out of the pressure relief valve every time the burner comes on to heat the water? It has been doing this for several months and my builder said his plumber told him it is normal.:confused: Also the temperature just...


View more questions Search