    Electronic ignition problem
    I have had installed 2 new honeywell gas valves, t5he are controlled by a honeywell 24v electronic ignition module I have also had replaced the igniter and sensor, when there is a call for heat stage 1 lights up fine and eventually stage 2 after about 10 minutes the ignter on one of the stages tries to spark again the flames on both stages are still on while this is happening. Is the igniter or sensor a problem are maybe the module. Any help would be appreciated.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Oct 30, 2011, 01:59 PM
    Sounds like you have replaced everything but the ignition module. If the igniter starts to spark while burners are lit, it seems it would be a flame sensing issue. Since you have already replace the atuall flame senser, I would think your next step would be replacing the complete control module that the flame senser wire hooks to. Sure sounds like a fualty module. The fact that the flame doesn't go out when the sparker start up again makes me leary. The flame should not stay lit if the flame isn't being sensed by the flame senser setup. I think you need to get a pro in there to diagnose the system.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Retrofit furnace to electronic ignition. [ 1 Answers ]

Can I retrofit furnace to use elctronic ignition; it now uses pilot light and Baso l62aa-5 control.

Furnace Electronic Ignition [ 4 Answers ]

I have a Coleman gas furnace with standing pilot light that I would like to convert to electronic ignition if possible. Model number is: 7655-856. If electronic ignition is not available, is there a high efficiency model that's a direct replacement?

Gas range/electronic ignition [ 1 Answers ]

I have a whirlpool gas range. Over the past two years the electronic ignition has stopped working approximately a dozen times. It may stay off a couple hours to a couple of days. Then for some reason it will start working. All connections apear good. What do you think the problem is?:(

Electronic Ignition on burners, click but no spark [ 2 Answers ]

My six year old, well maintained Caloric Gas Range has sealed burners and electronic ignitions to light the burners. I clean this critter regularly after each cooking session, but over the years, three of the four burners have ceased to light. They make the click-click sound, and I have to light...


View more questions Search