    Hooking up two blower motors...
    I am hooking up two water to heat exchangers with fans. I need to know if I can wire the fan relays in parallel with the zone valves, so the fans start when the zone valves open.
    I am using time delays for the fans but know how to wire them, I just want to know if the relays can be wired and triggered at the same time the zone valves are opening.

    Thanks
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Oct 22, 2011, 07:21 PM
    I don't see why not as long as the supply wire is large enough and rated for the full load amps. The isolation relay with time delay is the way to go. Your on the right track.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Newmac wood furnace. Problems hooking up the blower wires. [ 0 Answers ]

I have a Newmac wood furnace. I am having problems hooking up the blower on the front of the furnace. I can see where the black wire hooks but I don't see any connection for the green and white wires. Any help would be appreciated. Thanks

General electric blower motors [ 2 Answers ]

Have a ge 5kcp39ng Wiring digram missing from side of motor. Please giveme wiring digram and were they go. Have a goodman airhandler a48

Bryant 383K blower motors [ 1 Answers ]

Are the bearings on the blower motor for a Bryant 383K furnace internally sealed, or can they be lubricated periodically? I disconnected power to my furnace and reached into the blower compartment to spin the fan and it seems to take a little bit of effort to get it to spin. Bad bearings? Replace...

Hooking up inside blower motor [ 4 Answers ]

I have a Emerson direct drive blower with the following wires: white, black, red, blue, brown with white strip, brown. The problem is that the wires don't match the color coded wires on the old unit and I have no idea which wires go with the wires in the furnace. Can you help?

Wiring up blower motors in woodburner [ 7 Answers ]

Hi, I'm new here so bear with me. This spring, I removed my woodburning insert(really old with no info about manufacturer) for major cleaning and some chimney repairs. I removed two 110 volt motors, a 110volt thermostat, and one 110 volt on/off switch from the stove(thinking I could remember how...


View more questions Search