Carrier Weathermaker 8000 intermittent operation
Hello,
I have a Carrier Wethermaker 8000 gas furnace. Over the past week or so, I've noticed that the temperature in my house drops into the low 60's (I usually keep the thermostat on 68/69) and the furnace never kicks on. The thrmostat itself seems to be OK. The problem is intermittent at this point.
When this problems occurs, I go to the furnace and toggle the on/off switch to the transformer, the furnace will then fire up and run fine. My first thought is that I've got a flakey transformer. Any thoughts?
Thanks,
Ken
|
|
 |
New Member
|
|
Oct 29, 2007, 12:27 PM
|
|
Hi there
Did you ever get an answer for your problem? I have the same issue with no answer?
Kyle
|
|
 |
Junior Member
|
|
Oct 29, 2007, 06:05 PM
|
|
Read the faq section, In this case I'm thinking the flame sencor may be dirty.
But I'm not there so its just a guess.
|
|
 |
New Member
|
|
Dec 26, 2007, 11:59 AM
|
|
 Originally Posted by kewasiuk
Hi there
Did you ever get an answer for your problem? I have the same issue with no answer?
Kyle
Did this resolve your issue. I seem to have a similar problem. The on/off switch doesn't restart it anymore, it used to. Now I have to take the bottom and top covers off which resets the furnace and then runs fine for a day until it I have to take the covers off again. I wonder if the flame sensor needs to be cleaned as well or it's something else.
|
|
 |
New Member
|
|
Dec 26, 2007, 02:38 PM
|
|
Hi Kyle,
I'm not sure if someone from this site answered it or not. But here's what I did to fix it:
1. Take off the upper cover on the furnace to access the burner unit. (Mine has four burners).
2. On the leftmost burner, you should see what looks like a wire protruding on the far side. (From what I understand, this is some type of heat sensor).
3. Run a piece of emory cloth or sanpaper over it a few times. This will knock off any dust or contamination that may have accumalted.
4. Also, make sure you have clean air filter insatled.
This worked for me, hopefully you'll have the same result.
Good luck,
Ken
|
|
 |
New Member
|
|
Dec 26, 2007, 02:41 PM
|
|
Oops, I should give credit where credit is due...
Jugallojed came up with the fix... :-)
|
|
 |
Ultra Member
|
|
Dec 26, 2007, 03:13 PM
|
|
 Originally Posted by kewasiuk
Hi there
Did you ever get an answer for your problem? I have the same issue with no answer?
Kyle
When you need to reset the furnace and it starts again it is a safety feature in the circuit board. If the furnace fails to run like it should, the circuit board does what's known as a lock out. There should be a window in front of the PC board. In the window there is a red LED that will flash a code when it is locked out. Say the code is 2 short flashes followed by 2 long flashes. Look at the legend on the blower door and it will tell you why it locked out. Best of luck.
|
|
 |
New Member
|
|
Dec 27, 2007, 07:21 AM
|
|
I located the LED, the codes on the cover, no flashes of codes, the furnace was off for a bit when I got there. I had the same HVAC friend come by and take he said something about overlimit heat.
|
|
 |
New Member
|
|
Dec 27, 2007, 07:25 AM
|
|
I think the code for overlimit is 34. I didn't see it myself on the LED. I know, frustratubg.
|
|
 |
New Member
|
|
Dec 27, 2007, 12:42 PM
|
|
I just joined and have the same problem with a Carrier 58SXC080 furnace. The furnace was installed in 1992. The combustion blower failed under warranty the first season. The PC board failed and was replaced about 5 years later.
From what I can tell when it fails now the hot surface ignitor heats up but the gas valve doesn't open. Ignitor power is cut but there is no flame. It cycles through 3 attempts to get a fire going by powering up the hot surface ignitor. After the third failure it shuts down and locks out. Power-cycling the furnace switch (off-on) causes it to run a brief purge with the blower, then run the combustion chamber blower, then attempt another ignition. It will usually start then but at the next call for heat I often have the same problem. I replaced the flame sensor even though the symptom doesn't fit a flame sensor failure. I also replaced the thermostat.
I'm about to buy a replacement PC board. This will be my second and I paid over $400 for the first replacement by the HVAC company that installed the furnace. I found an on-line supplier for under $200.
|
|
 |
New Member
|
|
Dec 26, 2009, 08:57 PM
|
|
Thanks for the help in this, I asked a friend he stated to pull the sensor out removing one screw and disconnecting one wire. Clean the sensor with steel wool. It has been a couple of days and it is working. He stated the sensor is there to ensure all burners light if it is dirty it will cause the error shutting down for 3 hours. Thanks again for the help in figuring this out.
|
|
 |
New Member
|
|
Dec 13, 2010, 01:22 PM
|
|
I have been having this same probem with the same furnace model. I limped through last winter just throwing the on/off and it might be fine for weeks or only for a day. It is now doing it again. Had it serviced a few times last year with no luck. Just had a service tech tell me it is a known problem with this model and there was a part you could buy specifically for this issue on this furnace but it is now discontinued.
|
|
 |
New Member
|
|
Feb 11, 2012, 02:57 PM
|
|
Hello,
I had a similar issue with intermittent operation on a Carrier Weathermaker Infinity. We went through all of the above steps with checking the flame sensor but had no luck. We finally decided we would disconnect the hose to the heat exchanger and we noticed that there was a build up of a small amount of water in the heat exchanger causing the furnace to shut off prematurely. Took out the hose and blew it out. Reconnected the hose and furnace started up like a charm! The water had accumulated due to a malfunctioning water pump motor that was attached to the furnace to expedite the flow of moisture out.
Hope this helps!
|
|
 |
New Member
|
|
Jan 24, 2013, 03:34 PM
|
|
Check the fleu pipe for any obstructions, I found three dead small birds in mine.
Once cleaned it operate great now
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Carrier Weather Maker 8000 flame sensor
[ 10 Answers ]
Hello,
I have a Carrier weather maker 8000 and have received error 34. I would like to find the flame sensor so that I may clean it but don't know what it looks like. I have surfed the site and am unable to find it. Can anybody help with this.
Thank you in advance,
TripleT
What to do with $8000
[ 13 Answers ]
Hi I'm getting married in march and my fiancée has $8000 dollars in an AG EDWARDS that's doing nothing.any ideas what we should do with it?
Weather maker 8000 R-W
[ 1 Answers ]
We have a weather maker 8000. And we have gotten a code 12 from the L.E.D light. The code means R-W closed. My question is what is the R-W and where is it located on the Weather Maker 8000?:confused:
Intermittent blower operation
[ 3 Answers ]
Hello, I have a Janitrol model A30-08 furnace. On the AC side, when the thermostat calls for cooling, sometimes the blower kicks on, sometimes not. The evaporator coils always cool down (to the point of icing if I don't intervene), so that part is working fine.
When the blower doesn't come on,...