    #1

    Oct 6, 2011, 01:54 PM
    How to fix Goodman GMP125-5 furnace?
    I have a GMP 125-5 Changed hi limit and board. Soon as it is powered up the blower comes on even with the T-stat in the Off position
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Oct 6, 2011, 06:54 PM
    You have more than one limit switch did you check them all? Did you check for polarity correct line voltage on the control board? Last but not least did you check the low voltage fuse on the control board to make sure it wasn't blown?
    JonesHVAC's Avatar
    JonesHVAC Posts: 173, Reputation: 12
    Junior Member
     
    #3

    Oct 11, 2011, 05:40 PM
    You still have an open limit. Could be an auxiliary limit... Check for continuity on all of them.
    tenwen's Avatar
    tenwen Posts: 1, Reputation: 1
    New Member
     
    #4

    Nov 3, 2012, 03:03 PM
    Hi
    I have a goodman circuit board GMP 125-5 and recently does not have heat.
    The "ignitor" glows red.. but not spark on the sensor (bought a new one ) and the circuit board has 1 red LED that is on. Any suggestions will be helpful.
    Thanks in advanced
    And by the way.. A/C works fine

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Goodman GMP125-4. [ 1 Answers ]

Yesterday replaced the gas valve; today furnace worked a few times, now flames will not ignite; furnace attempts to turn on burners when it doesn't, it cycles off and give me 9 (nine) blinks. I'm thinking mother board; still trying to narrow down problem. Any suggestions?

Goodman gmp125-5 won't ignite. [ 1 Answers ]

I have a goodman gmp-125-5. The igniter ignites but the gas valve doesn't turn on. How do I trouble shoot to determine the problem ? I get a slow blinking light that I interpret to be a "1" on the mother board indicating a problem with ignition.

Goodman gmp125-5 motherboard shorts [ 1 Answers ]

I have a Goodman furance that I have replaced the motherboard 3 times they last about 6 months. Every time it happens the board blinks 3 times which means a vent issue but when I check the switch current its correct. We do have power outages. I also noticed some discoloring were the plug(runs from...

Goodman GMP125-4 starts up but does not ignite [ 3 Answers ]

I have a Janitrol / Goodman GMP125-4 gas furnace. Two years ago we replaced the motor, capacitor and the venter blower assembly. Last year (Nov 2006) we replaced the thermostat with a Honeywell programmable thermostat and then followed that with replacing the original integrated circuit module...

Goodman GMP125-4 3 times light flash [ 1 Answers ]

Hello I have a old GMP125-4. That what's going on : Thermostat in my room sending signal to furnace.Motor starting work and then is nothing... I can see trouble code (flashing light) it is 3 flashes and long pause, again 3 flashes and pause... Do somebody know what that code is mean ? - I...


View more questions Search