    Is 4.0 Triplex power feeder OK for 320amp service?
    I am upgrading a business from a 200amp service to a 320amp service in order to accommodate a 120amp tank-less hot water heater. I know that I need to replace the 200amp meter-base with a 320amp meter-base and K4892 kit. My question is: Will 4.0 Aluminium Triplex Power Feeder Cable be OK, or do I need to upgrade to something like a 350 MCM copper Feeder? Thank you in advance to anyone that can answer this before I get to a 2011 NEC book tomorrow, The Huntsman
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 4, 2011, 04:16 AM
    The utility's drop is NOT your responsibility, and it is NOT under the NEC's jurisdiction.

    I have seen 1200A services fed with 250mcm AL triplex and worse. So I would not be concerned.
    thehuntsman's Avatar
    thehuntsman Posts: 4, Reputation: 1
    New Member
     
    #3

    Oct 7, 2011, 05:39 PM
    Thank you stanfortyman. Here in MO I am required to supply feeder, weather head, and meter base. Ameren MO then connects service to the 36" line hanging from my weather head. I fully agree that it should be their responsibility to connect all of the way to the base. I have used the 4.0 with no problem before but did not know if the 2011 NEC had changed that. I appreciate your response and feel confident to go on with the installation. Sincerely, Joel H.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 8, 2011, 04:22 AM
    I see on page 30, note #1, of Ameren requirements:

    http://www.ameren.com/source/ConstSe...viceManual.pdf

    1. Overhead service drops and the connections at each end of the service drop will be owned, installed, and maintained by Ameren.

    You should consult with Ameren about this.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Oct 8, 2011, 05:07 AM
    Quote Originally Posted by thehuntsman View Post
    Here in MO I am required to supply feeder, weather head, and meter base. Ameren MO then connects service to the 36" line hanging from my weather head. I fully agree that it should be their responsibility to connect all of the way to the base.
    No, that's not what I meant.
    The "service drop" is only the overhead to the structure. From the weatherhead down to the meter is almost always customer responsibility.
    thehuntsman's Avatar
    thehuntsman Posts: 4, Reputation: 1
    New Member
     
    #6

    Oct 9, 2011, 07:14 PM
    Thank both of you tkrussel and stanfortyman. You both were very helpful. It seems as if it just depends on which engineer comes out to inspect and where the installation is. Either way, the weather head and meter base are installed with the head being 24" above the roof line and 3' of 4.0 hanging from it. I will call Ameren MO Monday AM for service hook-up. I really appreciate your immediate responses to my question. I wish you all much prosperity, Joel Huntsman

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

What size aluminum to use, triplex? [ 8 Answers ]

Hello, I am running a subpanel in my detached garage, 240v 100 amp panel. Distance is 170 ft. Direct burial, no conduit. Wondering what size/type aluminum to go with, 2/0 or 4/0, to comply with NEC code? By code I need the 4th (ground) wire because I will also be burying cable and data wire. ...

Installing 320Amp meter with 2 200A panels - Michigan [ 5 Answers ]

I have an electrician coming out to look at this, but I am curious to see what other have to say. I called Detroit Edison and they were of no help. I did get some information from DTEs website on meter installation requirements, but it doesn't answer all my questions. As stated in the title, I am...

Code compliant to compression splice aluminum feeder to copper feeder [ 15 Answers ]

Is it code compliant to compression splice aluminum feeder to copper feeder

HVAC issues in triplex [ 7 Answers ]

I own a very old home that was converted into a triplex during the housing shortage in the 40's. At some point a central heat/air conditioning unit was installed which services the entire home, and where both cold air return ducts are located in only one of the units (the larger side that I...


View more questions Search