YORK DIAMOND 80 Not Staying Lit. = No Heat blowing.
[ 8 Answers ]
Hey you I have a York Diamond 80 - I don't have furnace model no. but I do have the Johnson Control board's model no. G91G951ADB-1403 (part no 031-01234-000). The problem: When I try to run the furnace the combustion blower, glow coil, and the 5 ports (burners) function. However the burners...
Heat pump never turns on, handler blows continuous with no heat except with AUX heat
[ 2 Answers ]
10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...
Heat Pump blows 5amp fuse when switching between defrost & back to heat. Them Heat work
[ 3 Answers ]
I have a Carrier Heat Pump System. It’s about 5 years old and has functioned OK until this Christmas Eve. One problem is the condensing unit is not kicking back on after it goes into defrost mode. I found a 5AMP fuse blown in the attic unit and once replaced it functioned. At least for a day or two...
Central heat not staying on
[ 0 Answers ]
My central unit heater will not stay running in auto, but will run if switch is put to on. I changed the thermostat to an electric one. It worked for a day & then started the problem again. It will run for about 10 secs then shut off.
Heat strips staying on without 24 volts connected
[ 1 Answers ]
I can't not figure out what is causing my heat strips to stay on. I have removed the t-stat wires and the condsener wires from the air handler. Changed out the fan relay and the heat squenser, but when I put disconnect back in the strips still come back on. I believe that the limit switch's ... View more questions Search
|