    Running a new 120 V underground line for pond fountain?
    I'm wanting to install a new 120V service to my pond to run a fountain, lights, recepticles, etc.
    Here are the facts. Any opinions on what I should install would be appreciated.

    The line will come off our house 200A Breaker Panel.
    The pond is approx. 600' away.
    The fountain runs 7.5 Amps.
    Continuous service
    Copper cable.
    Looks like I should use a #6 or even #4 AWG. To stay within voltage drop.
    What is recommended for underground cable Mfg. And where to buy.
    What concerns do I need to concern for the Breaker Panel?
    I'm thinking of a 15 Amp breaker.

    Any help would be appreciated. I do electrical work but it is all control wiring for machinery so my supply side experience is limited.

    Thanks, Thackery
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 28, 2011, 04:34 AM
    Using a voltage drop calculator arrives at a #4 copper wire for a 2.3% Vd:

    1 conductors per phase utilizing a #4 Copper conductor will limit the voltage drop to 2.30% or less when supplying 8.0 amps for 600 feet on a 120 volt system.

    This allows 8 amps for the pump alone.

    Copper is expensive, and I doubt a direct buried cable is available. You can use wire THHN/THWN insulation and PVC conduit.

    Readily available is #2 aluminum 4 wire URD cable, that can be direct buried. Conduit would be recommended if the soil is rocky or provide an easy method of replacing later, or add more protection of the cable.
    ThackeryOhio's Avatar
    ThackeryOhio Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 1, 2011, 10:42 AM
    Thanks for the answer TKRussel, I have found several sources for the #2 URD-AL cable. Looks like about $1000 for a 1000' roll + shipping.
    I figured I would buy the 1000' roll and have the remainder for other buried cable projects I have coming up.

    I need advice on breaker panel capacity. Basically I don't know how to calculate how many breakers/amps I can use in my 200 amp service box. Where would I find the calculation rules for a panel?
    I'm searching this site for information.

    Thanks, Thackery

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Required wire for sub-panel, 400 ft, underground, 100 Amp, 120 Volt [ 5 Answers ]

Hello, I recently purchased a property which currently has electrical service running into a solitary shed. 400 feet away from the shed is an old foundation I would like to build a cottage on. I'm trying to figure out what it may cost me to run power underground from the shed to the proposed...

Can I connect a 120 line to an existing 240 line? [ 1 Answers ]

I have a 240 line coming to a cook top and would like to connect 2 120 outlets to that, if possible.

240/120 volt single phase (80 amp load) underground 180 feet [ 1 Answers ]

What is the recommended wire size to allow the use of either 2 hp radial arm saw or a stick welder plus 20 amp continuous lighting load.

Running utilities underground [ 1 Answers ]

Hello, My wife and I are planning to build a house starting this Spring. We have land, and will be building a good ways from the main road (about .5 miles). We are interested in running all utilities underground, like you would see in some housing developments, but I don't know where to start...

Running downspouts underground [ 1 Answers ]

Can someone please give me some guidance on the best way to tie my gutter downspouts into some underground drainage so the water will not just pour down my yard on top of the lawn? Also want to make sure the pipes avoid getting clogged over time to avoid digging it all up again.


View more questions Search