    My ac unit reads high side 230 low 28 temp outside 91 why don't it cool
    Ac unity reads 230 high side 28 low side outside temp of 91 why don't it cool
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Aug 22, 2011, 04:01 PM
    Suction side reading is way to low, should be well above 55. Could be low on refrigerant, or plugged filter drier, piston(orifice) or faulty txv valve. Many options here. Near impossible to trouble shoot on-line. Probably time to call in a trained a/c tech.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

The high pressure side and low pressure side of my ac unit are at 115 lbs, what do I [ 4 Answers ]

I have a Goodman ac unit at my house,the high pressure side and low pressure side are equal at 115 lbs. How do I solve this problem, or what do I do to fix this problem.

Heat pump low side and high side lines both warm I have comfortmaker 13 seer [ 2 Answers ]

Both my high side and low side are reading 115 psi. High side line is warm and low side is warmer, not getting sufficient heat what could be the cause? Could it be the valve?

R22 LOW SIDE and high side same pressure 120psi [ 2 Answers ]

r22 LOW SIDE and high side same pressure 120psi. Condensing unit works for 15 seconds and then stops

New AC unit won't cool temp past 77 F [ 10 Answers ]

This is an upstairs 2 ton unit for aprox 1300/1400 sq ft. (central) Old unit (same as above) use to get the upstairs as cold as we wanted, But so far this summer it did not, After repeated service to the unit w/o any improvement, We had it replaced. The old unit started running non stop...


View more questions Search