    Can you run pvc instead of emt in a multi shopm bldg. some of the circuits have been run in bx.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 16, 2011, 02:46 AM
    Should be able to use PVC, best to check with your local inspector to determine if there is some reason, such as place of assembly or fire rating of the building that requires only metal raceway.