    How to connect shower to pvc sewer?
    I am connecting a 2" PVC steam/shower drain into the main 4" PVC drain under the basement floor. The floor has been opened up with the 4" PVC exposed. We will use a "Y" Tee to make the connection. We are 5 feet from the 4" main.
    1) Do we need a vent?
    2) What is the correct type of mechanical joint to use under ground when we cut the 4" main?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Aug 14, 2011, 03:21 PM

    Let me run it for you. Will a permit be pulled for this job?
    From the 4"main you will cut in a 4X2 wye or combination wye and eight bend. Making your slope you'll 1/4" to the foot you will pipe up next to the 2" trap where you will roll up a 2" wye or combo and run up a 2" vent pipe that will either go out the roof or revent back into a dry vent to roof.
    From the 2" fitting you may connect the trap and the shower drain.
    You did know that every trapped fixture HAS to be vented didn't you? Did that answer your question? If not click on bark. Good luck with your project, Tom
    DIY Phil's Avatar
    DIY Phil Posts: 2, Reputation: 1
    New Member
     
    #3

    Aug 14, 2011, 03:50 PM
    I always thought f you were close to the main you did not need to vent.
    We are 5 ft from the 4" main and the trap will be under the concrete basement floor
    Yes a permit will be issued. Need to get it right the first time.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    Aug 14, 2011, 06:34 PM

    DIY Phil: You are not saying what Plumbing Code you fall under. I work under UPC. Here, you need a vent for every plumbing fixture.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Aug 15, 2011, 07:52 AM

    I always thought f you were close to the main you did not need to vent.
    We are 5 ft from the 4" main and the trap will be under the concrete basement floor
    Yes a permit will be issued. Need to get it right the first time.
    No matter what code you fall under you are sunk by two plumbing mandates.
    1. Every fixture that has a trap MUST be vented**and**
    2. You can not discharge a major fixture ( such as in your 4" main) past a unvented minor one.
    Now Milo works under a stricter code,UPC then I do at SPC so I can't imaging that Milo would tell you any different since his code vents everything including the family dog.
    It's for sure if you've permitted this job the inspector's going to be looking for a vent on that shower of yours. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pvc to lead connect [ 9 Answers ]

I have a 1.5" lead stub to a cast iron waste pipe in a 1912 house. I am replacing all the drain pipe that leads into that stub. I find that a 1.5" PVC pipe slides over the lead and makes a pretty good slide fit. I plan to run a 45 degree fitting from the stub and go from there. My question is...

How should iI connect a wye to a 4" pvc sewer pipe [ 0 Answers ]

What is the best way to connect a wye to an stationary 4" pvc sewer pipe

Should I use cemented PVC or PVC sections for main sewer line? [ 5 Answers ]

I'm replacing the main sewer line for my 1850's house located in Quebec, hence cold winters and the risk of shifting due to freeze thaw cycles. The line was previously replaced, and is now a series of three feet long 6 inch concrete sections connected together. I was planning on installing PVC...

Fernco neoprene coupling to connect two PVC pipes instead of a pvc repair coupling? [ 3 Answers ]

Hi, A plumber was replacing some plumbing in our shower area. He connected two 2" PVC pipes that ran directly into each other with a Fernco Neoprene Coupling. In another place, he connected two 3" PVC pipes that ran directly into each other with a second Fernco Neoprene Coupling. In both cases...

How to Connect PVC to Concrete in Sewer Pipes [ 1 Answers ]

Hi! I am experiencing slow drainage in my main sewer and a plummer told me there are roots in the system. I dug a trench to locate the main sewer, which I found. It consists of 2 feet of 4" cast iron pipe that is then connected to concrete like pipes that are about 5.5 inches thick in...


View more questions Search