    Selecting Thermostat with proper temp. differential
    Hello -
    Recently I had Lux digital thermostat replaced. After several attempts with Honeywell tstats -- that were cycling the death out of my furnace -- had contractor install White-Rodgers 1f56-444 mercury-style tstat. After devouring this site, I learned to adjust the heat anticipator to 1.2 A, to get longer cycles, which I am understanding is more efficient. I'd still like less cycles. (Currently if it's set at 62 F, it will kick on at 61.8 F, and turn off at 62.2.)

    I recall the furnace cycling less with the old Lux. Is there a thermostat that gives you the ability to select longer, and less frequent cycles or ajdust the temp. differential?

    All advice would be greatly appreciated.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Feb 1, 2007, 02:27 PM
    Nothing more you can do with a mercury bulb stat. A good digital stat lets you set the CPH cycles per hour and differential, degree diference off and on.
    UpstateBabs's Avatar
    UpstateBabs Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 2, 2007, 07:57 AM
    Thanks for the input. Is there a specific digital thermostat that you had good experience with that allows a differential of 2 degrees or greater?

    I tried a 70 series digital White-Rodgers, but apparently contractor and supply company could not figure out how to increase the differential. They concluded that digital was too sensitive to drafts in house and I was better off with mercury.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #4

    Feb 2, 2007, 04:30 PM
    I like Honeywell, some of the other tech's don't. You must read the installers guide to set up these stats the way you need and want them to work. It needs to be a 2 stage heat model.
    UpstateBabs's Avatar
    UpstateBabs Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 2, 2007, 05:03 PM
    Quote Originally Posted by NorthernHeat
    I like Honeywell, some of the other tech's don't. You must read the installers guide to set up these stats the way you need and want them to work. It needs to be a 2 stage heat model.
    Thanks, NorthernHeat. I see a RobertShaw 2 stage digital that seems to fit the bill.
    dewey066's Avatar
    dewey066 Posts: 49, Reputation: 1
    Junior Member
     
    #6

    Feb 14, 2012, 02:06 PM
    Why don't you try a thermostat with adaptive-intelligence, such as the Honeywell Vision Pro 8000. When you first install it, it will automatically turn itself on in the middle of the night, and sense how long it takes for it raise the temperature. It will do this several times until it determines what heat anticipator settings are correct for your environment. I do HVAC for a living, and this thermostat has proved itself in many situations. These thermostats can be a little pricey, so be sure not buy one that is overkill for your system. They come in many varieties such as single stage heat/cool and multi-stage.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Temp set at 72 but temp won't go above 66 [ 2 Answers ]

We have a Lennox Pulse 21 furnace. Temp is set at 72 but the furnace stops once the temp reaches 66 degrees. Thermostat seems to be working. The seems to be a problem just when it is really cold (0 to 10 degrees).

Temp gauge showing temp, 2001 Chev Malibu [ 13 Answers ]

I have a 2001 Chev Malibu LS, V6, temp gauge is not showing any heat at all, not registering when I know the coolant is hot ? Veh has about 126000 mi on it, never been flushed out, thought I would attempt to flush myself but don't you think the problem might be a bad thermostat ? If so, where and...

Question about supply temp. & return temp. [ 3 Answers ]

The AC system produced supply temps. At 57-60 degrees on the first floor With a return temp. of 71 degrees. The second floor supply temp. is at 59 degrees with a return temp. of 72 degrees. I know there should be at least a 15 degree temp. difference from the supply to return. There was also an...

Selecting Blendolini Causes Choco-Banana Shake Hang! [ 2 Answers ]

Does any one have a copy of Microsoft Technical document Q157668? A friend of mine said it was 'pulled' after it made Microsoft look a laughing stock! I've tried contacting them about it,but they say it's no longer available.I wonder why? Best wishes, Nez.:D

How works a differential radioassay [ 1 Answers ]

Please could someone explain to me or give me www-links where is explained what exactly a differential radioassay is an how it works. Thanks in advance Stephan


View more questions Search