    Grounding bar and neutral bar together
    What should be done if the neutral and ground wires in same bar. In the panel box there is one bar with grounding wires and the white neutral wires together.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Aug 11, 2011, 05:22 PM
    Maybe nothing. Depends on how old the panel is. In days gone by, the grounds and neutrals were on the same bar. How old is the house and panel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Aug 12, 2011, 02:38 AM
    Age of a panel is irrelevant.

    Age of equipment is NOT listed in the National Electric Code.

    If the Main Breaker is in this panel, the neutral and ground bars are to be connected.

    If the Main Breaker is, for example, located at the outdoor meter, then the neutral bar in the panel must be insulated and isolated from equipment grounds.

    Does this panel have the Main Breaker located in it?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground bar and neutral bar [ 17 Answers ]

I was working on a rehab project, and the guy working on the wiring was installing both the ground wire and the neutral wire together into the ground bar or neutral bar, depending on the side of the circuit. I was always under the impression that ground wires to ground bar and neutral wires to...

Grounding Bar vs. Neutral Bar? [ 14 Answers ]

Hello all. I have extended the wires from an unused 240 outlet to the backyard for a spa via a sub-panel. I also hooked up a new grounding electrode near it to avoid having to run a fourth wire all the way back to the main panel. This fourth wire goes to the small grounding bar in the sub-panel...

Connecting Ground bar and neutral bar [ 6 Answers ]

I'm wiring an additional panel into a garage. It's connected to the Meter through a switch that switches the power between the company power and a generator. The main house panel is inside the house. I understand that the neutral and ground are connected in the "main panel" only and any subpanel...

Subpanel Grounding Rods and Neutral Bar [ 7 Answers ]

My main service panel is installed in a detached garage. Our new home is fed by a subpanel run underground from the garage. At the garage panel I have two ground rods and the neutral bar and ground bar in the panel are connected. At the house subpanel location do I need additional ground rods...

Why is the grounding and neutral bus bar connected in the sub panel? [ 1 Answers ]

I had an electrician come in and install a new sub panel in my house and wire up my kitchen. When he finished, I took it from there. Now that I have the rest of the house wired, its time to connect it all to the sub panel. Both the neutral bus bar and the ground bus bar (2 separate buses) seem to...