Ask Experts Questions for FREE Help !
Ask
    robwheat's Avatar
    robwheat Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 26, 2011, 05:24 PM
    No power on part of circuit
    I live in a mobile home. I have power on part of the circuit, but not all. The back bedroom is not working at all. When I check the voltage, I get 120 from hot to ground, but nothing from hot to common. Any ideas?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 26, 2011, 05:57 PM

    You have a loose neutral some where. Check all non working outlets and the last working outlet on that circuit. If the "Quick Connect" holes in the back of the outlets were used, move wires to screws. The Quick Connects are known to cause poor connections after a period.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Jul 26, 2011, 08:21 PM
    Hot to common-if you mean the neutral, you have a broken or disconnected neutral somewhere to the BR circuit. Check the last functioning outlet with a circuit tester, pull the outlet and subsequent outlets and look for a non connected neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Power on circuit goes on and off - circuit breaker not tripped [ 3 Answers ]

The power on one of our circuit serving the garage and outside outlets goes off, but the circuit breaker does not trip. It used to go off for a few minutes/hours and to come back on for days/months. Now it is seems to be off most of the time, but still comes back occasionally for a few minutes...

One circuit knocking out power to another circuit [ 2 Answers ]

I have a 3 wire grounded Romex cable connected to 2 circuit breakers by sending one black to a breaker and one red to another circuit breaker. They lead back to the kitchen wall where one gives power to the garbage disposal and the other gives power to the dishwasher. Both have GFCI protectors on...

Taking power from existing 3 way circuit to power another switch [ 5 Answers ]

Hi, I have another question, hope its not too confusing. I have an existing 3 way switch for the lights in my stairwell. I want to change the single gang box to a 2 gang box and add another switch to power 6 new can lights. Can I disconnect the hot (black) wire and add a pigtail and feed power to...

Loss of power on part of a circuit. [ 6 Answers ]

There are four outlets on my kitchen circuit. The first one appears to be working perfectly. When I plugged the AC adapter on my portable computer into the third of four outlets yesterday there was a spark. That outlet and the fourth one ceased to work. The circuit breaker did not trip. I...

Power goes out in part of house w/out tripping breaker Part 2 [ 2 Answers ]

How would I use a voltage tester? Would I go from outlet to outlet measuring the voltage? I've gone around the house and tightened outlets and opened the panel and tightened the screws that were not tight. I haven't seen the lights dim since I tightened everything. Thanks a lot! Gbrown