Ask Experts Questions for FREE Help !
Ask
    garciapu's Avatar
    garciapu Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 20, 2011, 11:45 AM
    National Electrical Code Online?
    I remember reading in the code that it is required to use a tapped Screw or a nut and bolt as a means to connect a bond to a metal building or beam. I have a situation where someone has used a Self tapping screw (tek-screw) to fasten a bonding jummper to from one metal structure to another.. what is the Code that says this isn't allowed. Thank you for your time.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 21, 2011, 02:50 AM
    At the beginning of Article 250 is the following, see #5:

    250.8 Connection of Grounding and Bonding Equipment.

    (A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following means:
    (1) Listed pressure connectors
    (2) Terminal bars
    (3) Pressure connectors listed as grounding and bonding equipment
    (4) Exothermic welding process
    (5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut.
    (6) Thread-forming machine screws that engage not less than two threads in the enclosure.
    (7) Connections that are part of a listed assembly
    (8) Other listed means

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

National Electric Code Online? [ 1 Answers ]

What is the electrical code for a/c ciruits how many a/c can go on a 120v 20a circuit

Free online copy of the 2008 national electrical code (nfpa 70) [ 6 Answers ]

National fire protection association

National Electric Code Online? [ 5 Answers ]

What is the ampacity of a #3 aluminum conductor in free air

National Electrical Code Online? [ 2 Answers ]

What is the height requirement from the floor for 110V service recepticles for class B hyperbaric chamber facilities?

National Electrical Code Online? [ 7 Answers ]

What are the grounding requirements for water meters with metal underground watger pipeing coming into the building?


View more questions Search