    Changing service
    Changing service disconnect. Service cable (1/0 aluminum) underground service is short by 2 ft for termination in new disconnect. Is it code compliant to splice (compress,butt) #1 copper(thhn)?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 15, 2011, 04:33 PM

    Please be a little clearer.

    What service are you changing?

    Are you talking about the conductors from the transformer to disconnect? Or from the disconnect to main service panelboard?
    chuckr97's Avatar
    chuckr97 Posts: 5, Reputation: 1
    New Member
     
    #3

    Jul 15, 2011, 04:44 PM
    Comment on donf's post
    Changinging main serice disconnect. Conductors from xformer to disconnect (combo)
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jul 15, 2011, 05:36 PM

    If those conductors are connected to a Power Company transformer then they are the property of the Power Company, why are you changing them? You need their permission to touch those feeders.

    You do realize that you would be working on live, unprotected conductors that could very easily kill you, don't you.
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #5

    Jul 15, 2011, 05:43 PM

    Yes, at least where I am at, the power company always does those wires. If they need to be changed for new service panel, they will change them out after you replace the house feeds
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jul 16, 2011, 03:28 AM
    Don and Fr Chuck, Chuck is not asking about replacing the underground wiring, he is asking about extending the wire.

    Chuck, this question I answered and gave you a product to use in this thread :

    https://www.askmehelpdesk.com/electr...er-587496.html


    There are pre-insulated mechanical connectors that use wrenches to splice large wire/cable, you are not limited to crimp style.
    chuckr97's Avatar
    chuckr97 Posts: 5, Reputation: 1
    New Member
     
    #7

    Jul 16, 2011, 01:41 PM
    Comment on tkrussell's post
    Thanks for help!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing from standard A/C units to inverters, is changing the copper lines mandatory [ 0 Answers ]

I have wall embedded copper lines through several properties that want to switch to the new daikin inverters for a/c. Must I change all these copper lines?

100amp upgrade to 200-amp is changing service wire all that needs to be changed? [ 2 Answers ]

I'm changing from 100 amp to 200amp breaker box. Is just a meter change all that is needed outside. I have the new service wire run. Does the Electric Co. charge for changing the meter?

Internet Company changing my service without telling me. [ 1 Answers ]

Hi my internet company had changed my serivce without telling me because they decided to no logner offer that plan and sent me a huge bill based on the new service. They said they sent a letter but I didn't get anything. Can they legally do this to me?

Changing from metered service on my shop to service from my house. [ 2 Answers ]

I’ve had the meter and 3 wire service cable removed from my shop. I’ve purchased 90 feet of 100 amp direct burial cable to run from the lower section of my home meter to my shop. Not being an electrician, I’m still trying to install this changeover. The direct burial cable has 4 wires. 2 larger...


View more questions Search