    Multiple neutral wires in one room running hot
    I have an issue in one room where the electrics suddenly no longer work and this issue is confined to only that room. Checking the wires to the electric and light boxes on multiple boxes, the white wire is running at 120V, and the hot wire is also running at 120V. I assume the issue must be a hot wire touching the white wire somewhere in the circuit, but welcome other thoughts and ideas on how to identify where the issue is, or anything else that may be causing the problem.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 10, 2011, 01:46 PM

    issue must be a hot wire touching the white wire
    Not necessarily. A neutral conductor has voltage on it when a light or outlet is on that circuit is in use. How are you checking voltage on the neutral? Normally your meter will not show voltage between the neutral and ground because the neutral and ground come together at the panel. In other words they are the same voltage. When you measure voltage you are measuring the difference in voltage of the two conductors.
    A meter showing voltage between neutral and the ground wire indicates an open neutral somewhere.
    If the neutral wire were in direct contact with a hot you would have a tripped breaker.
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #3

    Jul 10, 2011, 02:37 PM
    What sort of tester are you using?

    As far as I know what you're describing as "a white touching a black" somewhere would cause a short circuit and trip the breaker/blow a fuse, so I don't think this would be the problem exactly. (I could be wrong... ) Are you getting 120V from the white wire to the bare copper wire(ground wire)?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jul 11, 2011, 04:33 AM
    Sounds like an open neutral, this will cause you to measure 120 volts to ground.

    Need to check all connections beginning at the panel and through out the circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do you hook up the neutral or the hot wires first when tying into a service [ 2 Answers ]

When hooking up my house service cable to the local electric company do I hook up the neutral first or the hot wires. Thank you

Running multiple wires through holes in studs [ 12 Answers ]

Hello, I'm roughing in an addition and adding lighting and receptables (on separate 15 amp circuts) in accordance with NEC. But I cannot find anything that tells me if I can run more than one wire through the holes drilled vertically along the run through 2 X 4 studs (drilled 1 1/4" from the...

Running multiple Wires/How far apart? [ 3 Answers ]

Are there any gotcha or restriction in laying multiples wires along a rail, 120V 15 amp 14-12AWG? Concern on interference/shield? Can they be tie together or they have to be separate? How far apart can they be?

Hot neutral Wires [ 6 Answers ]

The wife turned on the toaster this morning and the thing quit and the receptacle was melted a bit,the breaker never tripped, fridges outlet does not work along with two in the living room. I replaced the melted receptacle. Still nothing on all four outlets the NEUTRAL reads 120 volts with ground...

Open neutral - 3 wires; white as hot? [ 1 Answers ]

OK, I've encountered an oddly wired outlet in my kitchen and am trying to replace it with a GFCI. I unwired the old outlet, taking note of where things were attached, just in case. I wired the GFCI acoording to instructions and then checked the wiring with a Sperry GFI checker. All seemed OK. ...


View more questions Search