Ask Experts Questions for FREE Help !
Ask
    rkjennison's Avatar
    rkjennison Posts: 3, Reputation: 1
    New Member
     
    #1

    Jun 1, 2011, 04:37 AM
    What causes AC compressors to explode on heat pumps?
    Can a TXV valve be the cause of an explosion of the AC compressor?
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #2

    Jun 1, 2011, 04:46 AM

    Don't most systems have both a high pressure and a low pressure sensor? If the expansion valve stuck shut along with a failure of the high pressure switch... the system could generate enough pressure on the high pressure side to cause a failure at the weakest link.
    rkjennison's Avatar
    rkjennison Posts: 3, Reputation: 1
    New Member
     
    #3

    Jun 1, 2011, 04:55 AM
    The AC tech put in a new compressor yesterday, charged the system, and started up the AC unit. The compressor ran for about 30 seconds and shut off. He tried looking everywhere to see if anything was loose or wired incorrectly and finally gave up and said the compressor was "locked up". He was going to order another compressor. Before he left he indicated that the TXV valve was probably the root cause of my compressor blowing up and the releasing of all refrigerant.
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #4

    Jun 1, 2011, 06:39 AM

    I'm not an HVAC tech by trade... I do have a license and know enough and have the equipment to repair automotive A/C systems. But the functions are the same.

    Since you had a compressor failure... was the system flushed between replacements? Compressor failures usually result in debris that needs flushed out to prevent a recurring failure.

    If too much oil was added to the system it will "slug" the compressor resulting in failure. Oil unlike refrigerant isn't compressible.
    rkjennison's Avatar
    rkjennison Posts: 3, Reputation: 1
    New Member
     
    #5

    Jun 1, 2011, 07:17 AM
    Comment on smoothy's post
    No, the system was not flushed. The tech mainly took out the blown compressor and said that all refrigerant had been released. He then started putting in the new compressor and relayed that he believed the TXV valve was the failure of my original compressor. I appreciate the input and your time explaining what you believe the problem is.
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #6

    Jun 2, 2011, 06:45 AM

    Some systems have filters installed in the refrigerant lines and the debris should have been caught if it did. But one can not assume there are filters installed. The larger the system from what I gather, the more likely filters are there. And in a heat pump because system flow is essentially reversed, you would need two.

    A receiver/dryer is not a filter, its function is to remove any trace amounts of moisture that might remain after the system was evacuated with a vacuum pump prior to refrigerant was put in. Moisture + Refrigerant = acid formation. Which will corrode the system from the inside.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Emergency heat ruud heat pumps? [ 1 Answers ]

Hi, Just bough a new house and it has a Ruud furnace and heat pump. The house was built in 1986 or so. On the thermostat I read heat and them Heat. What should it be set to? On heat only or Em Heat? Appreciate the advice.

Heat pumps in cold weather and using supplemental heat [ 2 Answers ]

Is it hard on a heat pump to use alternate heat source (kerosine heater,other) causing the heat pump to be off for long periods during the day and than allowing the unit to come on at night?

Heat pumps [ 1 Answers ]

I have a co-op apartment in a high rise in NYC. It has old GE zoneline 3000 heat pumps. One of the two works fine, the other wotks OK but it is noisy. The fan is just loud. Should I bother to try to repair this or should I just replace them. If I replace them should I get heat pumps again or should...

Heat pumps [ 3 Answers ]

What does the emergency heat do on a heat pump?