Ask Experts Questions for FREE Help !
Ask
    Eric in Mahwah's Avatar
    Eric in Mahwah Posts: 13, Reputation: 2
    New Member
     
    #1

    Jan 27, 2007, 11:36 AM
    Furance works once, doesn't restart
    A problem recently developed with my furnace. I increase the thermostat and I hear the furnace "click" on. I see the orange ignition light turn on and the flame begins to flow within 10 seconds or so and then the orange light fades away and the hot air flows - which I presume is normal.


    The heat continues until reaching the desired temperature. However, when the house cools, the ignition light turns on, the flame starts to flow and as the ignition light fades, the flames stop and cool air blows.


    If I power off the furnace, it always works correctly the first time the heat is on, but when it goes off, it never works correctly.


    Rheem Criterion II gas furnace.
    Model RCBA-2457GG14
    Serial M2897
    Forced air
    Approx 12 years old

    Please excuse me for the lack of technical terms.

    Thanks for any help.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Jan 27, 2007, 12:42 PM
    Check diagnostic light. If amber light "flashes" after the flame is established, the flame sensor is dirty. Flame sensor is a small metal rod located in front of the far left burner. Disconnect power, remove it with a 1/4 inch nut driver you'll probably need an extension. Clean it with fine steel wool or sandpaper, reinstall it, turn on power and watch diagnostic lights again.
    Eric in Mahwah's Avatar
    Eric in Mahwah Posts: 13, Reputation: 2
    New Member
     
    #3

    Jan 28, 2007, 09:07 AM
    Thanks. Are the diagnostic lights located inside the furnace?
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #4

    Jan 28, 2007, 09:25 AM
    Yes, on the circuit board in the blower compartment. There is a safety door switch that turns off the power when you remove the door. Often on Rheem furnaces there is a small viewing window in the door to see the lights through.
    Eric in Mahwah's Avatar
    Eric in Mahwah Posts: 13, Reputation: 2
    New Member
     
    #5

    Feb 9, 2007, 02:23 PM
    NorthernHeat - thank you very much. It was indeed the flame rod causing the problem. Cleaned it off and now everything works fine. Thanks again for the good, accurate advice.
    need-for-speed's Avatar
    need-for-speed Posts: 1, Reputation: 1
    New Member
     
    #6

    Feb 10, 2007, 02:27 PM
    Quote Originally Posted by Eric in Mahwah
    A problem recently developed with my furnace. I increase the thermostat and I hear the furnace "click" on. I see the orange ignition light turn on and the flame begins to flow within 10 seconds or so and then the orange light fades away and the hot air flows - which I presume is normal.


    The heat continues until reaching the desired temperature. However, when the house cools, the ignition light turns on, the flame starts to flow and as the ignition light fades, the flames stop and cool air blows.


    If I power off the furnace, it always works correctly the first time the heat is on, but when it goes off, it never works correctly.


    Rheem Criterion II gas furnace.
    Model RCBA-2457GG14
    Serial M2897
    Forced air
    Approx 12 years old

    Please excuse me for the lack of technical terms.

    Thanks for any help.
    Hi there ,

    Had the same problem with my 3 year old Rheem Criterion II and found that cleaning the flame sensor did the job perfect . Yellow LED would flash 3 times on statup then flame would go out , this would happen 2 to 3 times before the flame would finally stay on and the yellow LED would remain solid till the tempature was attained . Thanks to all for your helpful advise

    Best wishes
    Mark

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace won't restart [ 27 Answers ]

Furnace will not restart, when temp. drops. When you turn the furnace switch off and then on the furnace will restart. This will happen several times a day, if nobody is home for a while it can get pretty cold.

Tempstar smartcomfort two stage gas furance [ 2 Answers ]

The power went off in my area and the furnace has not worked since. I looked at the circutbreakers none were tripped. I turned the one switch I see on the furnace and still nothing. It will be some time before I can get service since there is a driving ban in my city right now can anyone give...

Humidifier and Furance Hookup [ 1 Answers ]

I have a pair of Carrier 100 BTU furnaces controlled by a Honeywell programmable thermostat. There is a Aprilaire humidifier with a completely separate control attached to the furnace. I purchased a fan relay Steveco 90-293Q to wire the humidifer inline with the furnace thermostat control. I would...

Ms works database to ms works spreadsheet [ 2 Answers ]

Have tried copy/paste but I get a message stating "make sure the destination area is as large as the info you wish to paste" .Anyone help please?

Problems on restart [ 1 Answers ]

Hi, newbi here, I just wanted to say hello and pose a question . I've learned a lot of useful information here in the past and I hope someone can help. I'm running MS xp Home Edition, I recently discovered a problem where upon restart , my desktop appears but my mouse and keyboard are frozen....


View more questions Search