    On what basis The VCB for a 33KV HT Panel can be selected?
    I want a little help in selecting a VCB for a 33 KV line, with three 1.5MVA transformers and the total load distributed in the LT side is about 4 kilo-watt?
    I want to design a panel in the HT side with appropriate VCB ratings feeding 33kv line to the three 1.5MVA Transformer.
    Attached Images
     
    manishsarkar's Avatar
    manishsarkar Posts: 2, Reputation: 1
    New Member
     
    #2

    May 15, 2011, 12:45 PM

    Sorry, the distributed load is 4mega watt not 4 kilo-watt.
    Newton1Law's Avatar
    Newton1Law Posts: 60, Reputation: 5
    Junior Member
     
    #3

    May 16, 2011, 09:47 AM
    You total Load is 4 Megawatts and you have a total trnsformation of 4.5 MVA. Based on the transformer capacity of 1.5 MVA at 150% or 2.25 MVA, the priamry current to each transformer is only about 40 amps. Any three phase VCB that you might buy that is rated at 33 kV will most certainly be large enough for the current load. They will most likely be 600, 1200, 2000 amp rated vacuum breakers. The next item you need to address it the fault duty they will be required to interrupt. If the fault duty on the load side of the VCB is say 10,000 amps, the VCBs will have to be rated to withstand 10kA, taking in to account the asymmetrical fault you may want to increase the rating to 20kA. VCBs are readly available for this application.

    Last, the type of relaying required would need to be reviewed. Will yo be using transformer differential realying to protect the transformers? What about harmonic restraint relays for when you energize the transformers under no-load conditions? Also, how are you protecting the transformers for an internal high impedance fault? Pressure differential or sudden pressure relays?

    A place to start might be:

    http://www.abb.com/product/db0003db002618/b648efb374db3fa0c125754e0046c50b.aspx?productLangu age=us&country=US

    Hope this helps,

    Newton1Law

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

33 kV VCB Breakers [ 2 Answers ]

What is the frequency of overhauling of 33 kV VCB breaker?

Reporting Cash Basis versus Accrual Basis Income [ 3 Answers ]

Please help, I'm confused. Music Company had the following transactions in March: a. Sold instruments to customers for $10,000; received $6,000 in cash and the rest on account. The cost of the instruments was $7,000. b. Purchased $4,000 of new instruments inventory; paid $1,000 in cash and...

M3-2 Reporting Cash Basis versus Accrual Basis Income: LO1, LO2 [ 3 Answers ]

Mostert Music Company had the following transactions in March: 1. Sold instruments to customers for $10,000; received $6,000 in cash and the rest on account. The cost of the instruments was $7,000. 2. Purchased $4,000 of new instruments inventory; paid $1,000 in cash and owed the rest on...

Reporting Cash Basis versus Accrual Basis Income [ 1 Answers ]

Forllowing transactions in March. Do both cash basis and accrual basis income a) Sold instrument to customers for $10,000; received $6000 in cash and the rest on account. The cost of the instrument was $7000 b)Purchased $4000 of new instrument inventory;paid $1000 in cash and owed the rest on...


View more questions Search