    Hvac conderser fan not starting
    Hi, my hvac system is a bit old, my main problem right now is that when the thermostat kicks in and starts the cool cycle, the fan starts as expected BUT... the fan condenser outside is not starting just doing a humming noise, like it is stuck, well yesterday I tried to figure out and manually give it a "push" and it got going like nothing... so everything went perfect, but today its not starting again, what does it need to be replaced?. the motor fan?. or is there anything else that might be affecting my system?
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #2

    Apr 26, 2011, 04:59 AM

    There is probably a motor starting capacitor that has worn out. Trace the wires from the fan motor and see if you see a round or oval can with several push-on connections. Replace with an equivalent part. Should be a $20 part or so.

    Make sure you disconnect the power before doing this work!

    Best of luck,
    WallyH
    pistofernandez's Avatar
    pistofernandez Posts: 5, Reputation: 1
    New Member
     
    #3

    Apr 27, 2011, 11:09 AM
    Thanks a lot for your answer!. found out it's a 40+5 capacitor and already ordered it, will give it a try...
    What should the reading on the terminals be for?. I haven't looked at it yet.. but noticed one has a C the one is 2 posts and another 3.. something like that...
    But what should I prepare for?
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #4

    Apr 28, 2011, 05:48 AM

    The capacitor is actually 2 capacitors in a single can. In your case one is 40 uF and one is 5 uF. One of the capacitors goes to the compressor motor and the other goes to the fan motor. Hopefully you have not yet removed the wires from the old one so that you can simply transfer them one at a time from the old to the new.

    For your information, the "C" terminal means "Common". This terminal is connected to both the fan and the compressor motors. That is, each motor will have 2 wires going to the capacitor can, and one from each motor will go to the Common terminal. The other wire from each motor will go to its respective 40 uF or 5 uF connection.

    Generally, the 5 uF side will go to the fan motor and the 40 uF side will go to the compressor. A lot of times, the terminals will be labeled, "Common (C)", "Fan (F)", and "Herm (H)". Herm is short for hermetic, or the hermetically sealed compressor.

    Here are a couple of good websites for reference:
    Air Conditioner Dual Motor Start Capacitor Replacement Instruction Guide With Pictures
    Capacitors

    I hope this information is helpful,
    WallyH

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Conderser fan motor quits on thermal overload [ 2 Answers ]

IT runs for about three or four min. and quits. The old motor would not run at all it's a new motor and capacitor. The contact voltages checked good. The only thing left is the thermister and the control board. The thermister does get pretty warm. Please help

Why does my hvac fan keep running? [ 1 Answers ]

I have an older, central H&A system with a fan that won't stop running. Heat & air both work fine, but once the house gets to the right temp, the unit will cycle off but the fan keeps running regardless of whether the fan is switched to "on" or "auto". Many times the fan will stay on for up to 4...

What is quieter a 3 blade or a 4 blade conderser fan [ 0 Answers ]

Is a 3 blade fan quiter than a four blade

Overheating conderser fan motor [ 3 Answers ]

My old condenser motor was overheating and stoping. I replace it with a new motor but it is overheating and stoping also


View more questions Search