    I need to run electrical in 3/4" Grey PVC conduit 1000'
    I need to run electrical in 3/4" Grey PVC conduit 1000' to operate a gate opener which is just a 24V A/C adapter 40VA and two lights (maybe 60Watts/ea). Can I get away with running #10, or do I need #8? Thanks for the help.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Apr 20, 2011, 11:18 PM

    If I calculated it correctly, you would need to use XHHW type cable.

    A 120 V / 20 amps feed would require a 2/0 - 2 wire plus ground cable.

    That would give you 113.6 AC volts at the end of the run with 20 amps.

    I'm sure TK will check my clacks for accuracy so please wait for his response.
    NBC455's Avatar
    NBC455 Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 20, 2011, 11:34 PM
    Wow, that will cost a fortune to run two lines. I can run 1000' low voltage wire, and install low voltage lights on columns as well. I thought some THHN #8 would at least power a couple of light bulbs. Can I run low voltage wire next to THHN stranded wire in 3/4" Grey PVC? Thanks for your help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Apr 21, 2011, 02:51 AM
    Assuming 2 amps , two, of load at 120 volts 1000 feet, you would need # 8 copper wire.

    120 watts of lighting is 1 amp, and allow 1 amp for the opener is how I arrive at 2 amps of load.

    I would deliver 120 volts to the opener, and have the 24 volt at the end of the circuit. Do not try to deliver the 24 volts 1000 feet.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Romex in PVC Conduit ? [ 26 Answers ]

Need to run #12 wire to my gate opener. Have 1" schedule 80 conduit in ground. Can I run 12/2 Romex through the conduit to feed the gate ? Or do I have to run individual wires. Thank You

12/2 NM-B Romex in PVC Conduit [ 4 Answers ]

Hi. I need to bring 2 new circuits from the panel in the garage to the basement. I would like to use 12/2 NM-B (Romex with ground) from the panel through PVC conduit to the basement. It is about a 12' run, then a 90 degree turn, then about another 10' to a spot below the panel. At this point it...

How to pull #12 through 3/4 pvc conduit [ 15 Answers ]

How is the best way to pull a #12 neutral and #12 ground insulated through 3/4 pvc conduit that already has 2 #12 black wires. I need to get rid of one of the black wires and replace it with the white neutral and green ground. It has at least 3 90 degree ells.

Painting PVC electrical conduit. [ 2 Answers ]

I am trying to paint gray pvc electrical conduit to match the color of the house. The house is painted with BEHR self-priming acrylic latex house paint for masonry, stucco, & brick. Is there a special primer for this project?:confused:

Can I run a electrical line in the same conduit as phone and cable? [ 9 Answers ]

Aloha All, I built a little 8'x12' office that is approximately 185ft from my main house. I was planning on running a electric, phone, and cable line in an underground conduit from my house to the office. Can I just use 20A romex for the electrical line that will be tapped off an exterior...


View more questions Search