Ask Experts Questions for FREE Help !
Ask
    m_abbott's Avatar
    m_abbott Posts: 1, Reputation: 1
    New Member
     
    #1

    Mar 29, 2011, 06:41 AM
    NEC question: Dose a lighting panel require a main breaker?
    Replacing 5 panels in a High Schoo (120/208v panels). All branch circuits feed lighting and receptacle loads. They are very old and also "main lug only". Do I have to have a main breaker in the new replacement panels? If so where is this in the code?

    Mike
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 29, 2011, 06:46 AM
    PER NEC, MLO panelboard is fine. A MCB in each panelboard is not required, but optional, as the panelboard will be protected by the feeder CB at the distribution board.

    You should be checking with the engineer that wrote the project specifications, and/or the LAHJ.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do I need a main breaker for A panel? [ 1 Answers ]

I have a main disturbution panel that feeds a panel in a new addition. The panel is a 3phase 480v and has 12 circuit breakers in it. My understanding is that since there is more than 6 it has to have a main breakers or switch to kill power in case of emergency. Since it have a main disconnect in...

What is always LIVE/HOT in main panel w/main breaker off? [ 4 Answers ]

We are going to be putting a dedicated 20A/12-2 wire receptacle in the basement for our treadmill. When we are putting in the new 20A breaker, we are concerned with what is 'live' in the service panel. I know the 2 service wires are hot before the main but is there a chance anything else may be...

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Main breaker panel [ 1 Answers ]

Hi, I'm looking for a 100 or 125 amp 30 or 32 space main breaker panel(not a mlo) and have been unable to find one. Can some one tell me where I can get one with the main installed? Thanks Jim