    GFCI options for bathrooms
    1 of my baths in a new addition will have a whirlpool tub. The tub pump needs a 20A and the add-on heater needs a 15A. Naturally these both need to be GFCI protected. Is it acceptable to use dead-front GFCIs located somewhere in the bathroom for these or do I have to use GFCI breakers in the panel?

    Also - the pump/motor and the heater are required to be grounded and bonded. The plumbing in this new addition is all PEX, so there is no copper to bond it to. Can I run a 8g wire from the ground lug down into the main service panel and attach to the main ground there?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 19, 2007, 09:30 AM
    Using deadfront GFI device for this purpose is exactly what they are for, so no problem.

    As far as bonding, no, do not run a #8 back to the panel. What needs to be done is use a #8 to connect any metal within 5 feet of the tub, either under, such as metal pipng, the heater, etc or any metal above the tub, such as metal handles, ladders,etc, and the #8 wire will terminate at the ground lug that you should find on the outside of the pump motor.

    Now you have all the metal in the vicinity of the tub "bonded". Since the motor is grounded through the green or bare equpment ground wire that is part of the branch circuit wiring that feeds power to the tub/motor.

    The equipment ground now grounds the pump motor, and grounds the bonding done.
    BigRed1500's Avatar
    BigRed1500 Posts: 70, Reputation: 8
    Junior Member
     
    #3

    Jan 19, 2007, 09:43 AM
    OK good to hear about the dead fronts, so I can return the $80 worth of GFCI breakers I bought last night. What are the requirements on placement of the dead fronts - within / outside 6 feet from tub, etc?

    Just to make sure I have this right on the bonding. The heater instructions say to run the wire from it to the ground lug on 1 side of the pump. Then the pump instructions say to run a second wire from the other side of the pump to a ground. So - if I've grounded the receptacle box that serves the pump and heater outlets (2 circuits) am I understanding you right that I can simply ground the pump back to that box? If so, how do you recommend that I connect that #8 wire to the ground in that box, or the box itself?

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 19, 2007, 01:13 PM
    Quote Originally Posted by BigRed1500
    OK good to hear about the dead fronts, so i can return the $80 worth of GFCI breakers I bought last night. What are the requirements on placement of the dead fronts - within / outside 6 feet from tub, etc?

    Just to make sure I have this right on the bonding. The heater instructions say to run the wire from it to the ground lug on 1 side of the pump. Then the pump instructions say to run a second wire from the other side of the pump to a ground. So - if I've grounded the receptacle box that serves the pump and heater outlets (2 circuits) am I understanding you right that I can simply ground the pump back to that box? If so, how do you recommend that I connect that #8 wire to the ground in that box, or the box itself?

    Thanks
    Yes the breakers are pricey. The GFI deadfront cannot be closer than 5 feet to the tub, other than that put them where ever you like, unless they can be located down under the tub where the pump is.

    No just run a #8 from the heater to the pump, the lug on the outside of the pump. If there is no other metal within five feet of the tub, you done.

    The bonding is grounded through the equipment ground that you bring to the pump along with the hot and neutral wire to feed the pump. So if you plug in the pump into a receptacle, the outlet needs to be grounded, anda 3 wire cord feeds the pump.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Help with Stacked Bathrooms [ 1 Answers ]

Hi there, I live in an 800 square foot slab on grade home with 1 bathroom. I am adding a second story and including a bathroom and laundry room on the second floor. I positioned the bathroom by the main stack and the laundry further away. I intended for the toilet, sink, and tub and washing...

Smells from downstairs bathrooms [ 5 Answers ]

Hi there I have been reading lots of various postings on bathroom smells but still have not found a solution that works for us. We have 4 bathrooms in our apartment - 2 upstairs and 2 downstairs. There is no problem or smell from the upstairs bathrooms. Downstairs we have been having problems...

Two Bathrooms [ 2 Answers ]

I am about to install a second bathroom and want two showers to work at the same time. I am replacing all plumbing but there is only 15mm feed to flat. What type of boiler etc is needed to run two showers and washing machine at the same time?

What are my options? [ 1 Answers ]

I have a B.A. in accounting and business (1996). I currently work for $11 an hour in the medical field processing Medicare/Medicaid claims for a private doctor. I would like to earn more money but am uncertain of the possibilities. Do you have any suggestions? I have considered starting my own...


View more questions Search