    Skoon86's Avatar
    Skoon86 Posts: 3, Reputation: 2
    New Member
     
    #1

    Feb 4, 2011, 10:28 AM
    Stage 1 skipped on zoned geothermal system
    Just added zoning to our 2-stage geothermal system. We are running with a Lennox ComfortSense 7000 touchscreen thrmostat, Honeywell zone control board and Climate master geothermal closed loop system. With the zone board I can now see which stage the pump in in and while zones 2 and 3 are going through the stage 1 for the appropriate time before calling for stage 2, zone 1 jumps instantly to stage 2. All three thermostates are set up the same with the stage 2 delay set for 20 minutes. Installer has looked at it and chaged the temp differential from 4 degrees to 0.5 degrees. Still jumping to stage 2 on zone 1. Doesn't seem right to me. Could a miss wired thermostat or zone control board cause this?
    Skoon86's Avatar
    Skoon86 Posts: 3, Reputation: 2
    New Member
     
    #2

    Feb 8, 2011, 04:18 AM
    Got it figured out. The humidifier ground wire was wired incorrectly into tha zone 1 t-stat. It was hooked into the y2 slot, thus whenever the t-stat called for humidification it triggered stage 2 heat. As it's been cold and dry, this has been happening for weeks. Problem so
    Lved.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Will a 2 stage thermostat work on a single stage system [ 1 Answers ]

My question is will a 2 stage heat/cool or a 1 stage cool 2 stage heat thermostat work on a single stage system? Thanks, Mike

Hot Water zoned heating system air lock [ 6 Answers ]

I have a Hot Water zoned heating system. All zones are flowing except for 2. The zones that are not circulating have air in them and they appear to have an air lock. I have Radiant floor heat on the first 2 levels of the house and baseboard heat on the 3rd floor bedroom. I had a...

Geothermal a/c & heating sizing for 5 ton system [ 7 Answers ]

I live on the east end of long island NY. Wish to install dx system in ground water which is about 54 degrees

Slushing noise in two zoned heating system [ 1 Answers ]

I have two zoned hot water baseboard heating. There is air in one of the zones (slushing noise). The zone lever is set on closed. I tried reversing one of the lever close valves, which put it in an open position. Then I drained using the blue drain valve. When all done, I turned the lever gate...

Zoned heating system problems [ 4 Answers ]

I need help with information about my current heating system, I will try to be as brief as possible. We built a 5200 sq ft duplex home (2600 each side), with 4 levels. The heating contractor told us he could put in 4 zones, one for each floor. We moved in late fall of 2006 and discovered the...


View more questions Search