    Humidifier wiring
    I have a York Natural Gas furnace that is brand new. I just purchased a GeneralAire Bypass humidifier Model 900. The humidifier came with the E2 controller.
    I looked at the wiring diagram on both the furnace and the humidifier and the E2 humidistat controller and I am somewhat confused on how this humidifier will activate.
    The way I suspect the humidifier to work is that the water valve will actuate when the furnace is blowing, this will wet the screen and air will blow through it. But I don't see any connection between the furnace and the humidifier. How does the humidifier know that the furnace is blowing?
    The wiring for the humidifier and e2 controller shows 24V coming to the controller, and going out to the humidifier. Additional input is a temperature sensor.
    This just doesn't make sense to me.
    Am I thinking wrong?
    Ed
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Jan 16, 2007, 10:26 AM
    My furnace has a terminal to supply power to a humidifier when the blower runs, check yours. If not, you could tie into the W terminal of the furnace. The other wire goes to the com terminal.

    The humidifier could also have a switch activated by the moving air. If so, take the humidifier power off the R terminal.

    The temperature sensor could also activate the humidifier when it has warm air moving by it.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #3

    Jan 16, 2007, 04:30 PM
    A current sensing relay, hooked up to the heating speed of the blower, is the easiest way to make this work.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Aprilaire 700 Humidifier [ 6 Answers ]

I am installing a Aprilaire 700 Humidifier on a Goodman GMNT gas furnace the Furnace control board is a white rogers 50T 35-730 it has separate hum 24v Terminal and hum 120v terminal the Aprilaire 700 Humidifier includes a built in 110v to 24v transformer which one should I connect it to and also...

Humidifier questions... [ 2 Answers ]

Hello everyone - I have a humidifier question - actually a few. This will be my second winter in my house. We have a natural gas furnace. There is no humidifier. I've noticed a small amount of condensation on the windows, and therefore assume I don't have a need for a humidifier. However, my...

Wiring humidifier and humidistat [ 1 Answers ]

I have a he360a honeywell humidifier and a h8908b humidistat. If I plug the 120v cord into a outlet can I just run two wires from the humidistat to the humidifier. Would that work properly. The bow that the humidifier came with was open an didn't have all the directions. Could you tell me how to...

Humidifier, wiring the control [ 1 Answers ]

I have just installed an Aprilaire 700 Humidifier. I seems to work in the "test or reset mode" but that's all. I found the 24 volt transformer, as well as all the other thermostat wires. Some of the thermostat wires have voltage and some don't . This is depending on what the gas furnace is doing...


View more questions Search