    Heat pump
    The motor on my heat pump went out. I have read that if your heat pump has been shut down for more than a hour you cannot turn it on right away. We replaced the motor is it okay to just turn it back on?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Feb 1, 2011, 03:28 PM

    To over-simplify things, if a refrigeration system (a heat pump is a refrigeration system) is shut down, it should not be restarted in less than 5 minutes. If your heat pump has a crankcase heater and that has been shut off for half a day or so I would recommend whatever the manual says. If no crankcase heater, then start it up.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Installed a honeywell pro6000 stat on a carrier heat pump, cooling mode is heat pump [ 2 Answers ]

Installed a honeywell pro6000 stat on a carrier heat pump, cooling mode is heat pump

I have a Carrier 24HNA636A310 Heat pump. Does the Heat pump mode run on both speeds? [ 0 Answers ]

I have a new Carrier Infinity 25HNA636A310 compressor. Does it run in both speeds when in heat mode

Heat Pump blows 5amp fuse when switching between defrost & back to heat. Them Heat work [ 3 Answers ]

I have a Carrier Heat Pump System. It’s about 5 years old and has functioned OK until this Christmas Eve. One problem is the condensing unit is not kicking back on after it goes into defrost mode. I found a 5AMP fuse blown in the attic unit and once replaced it functioned. At least for a day or two...

Is a heat pump with emergency heat a multi stage heat pump [ 1 Answers ]

I am trying to replace the thermostat for my heat pump the one I've got seems to be running the emergency heat only. All wires were connected as they were in the old one. Is regular heat and emergency heat considered multi-stage? If so, I need another thermostat... please advise.


View more questions Search