    yahtzein Posts: 5, Reputation: 1
    New Member
     
    #1

    Jan 27, 2011, 05:00 PM
    Trane heatpump defrost problems
    Have a XT1000, it'll run either 45 minutes or 3 hours (guessing 45 min checks every time) and sometimes it'll then frost, other times (most) it will turn off the compressor, the fan will keep running, but no defrost. If left alone if start back up after 45 minutes if it is left alone. What could be the problem? I suspect the defrost board...
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Jan 27, 2011, 07:47 PM
    Is ice starting to build up on the condenser coil(1 inch or so)? If so it may be just a simple defrost thermostat going bad. Not to rule out the logic in the control board going bad. If you have a lot of ice build up on the coil. It will be the defrost control board or defrost thermostat going bad.
    yahtzein's Avatar
    yahtzein Posts: 5, Reputation: 1
    New Member
     
    #3

    Jan 28, 2011, 02:19 PM
    Comment on T-Top's post
    No, I think it engages the defrost often enough since its never had ice buildup, just frost. I checked the defrost sensor plug into the board and its loose. I'm assuming this is most likely the problem.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Jan 28, 2011, 05:14 PM
    If you have no ice build up on the condenser coil the defrost control board and defrost thermostat is working. Is it keeping the temp in the house of what you have it set on?
    yahtzein's Avatar
    yahtzein Posts: 5, Reputation: 1
    New Member
     
    #5

    Jan 28, 2011, 05:37 PM
    Comment on T-Top's post
    Right now the temp is set to 67 its 65 inside and the heat pump should be putting out air (warm), but its only room temp air coming out. The compressor is off, but the fan on the unit (outside) is running.
    yahtzein's Avatar
    yahtzein Posts: 5, Reputation: 1
    New Member
     
    #6

    Jan 28, 2011, 05:38 PM
    Comment on T-Top's post
    It'll do that for 45 minutes and then the compressor will start up again and put out heat. I have the aux off right now to diagnose the system a bit with a temp sensor at the closest vent
    yahtzein's Avatar
    yahtzein Posts: 5, Reputation: 1
    New Member
     
    #7

    Jan 28, 2011, 05:39 PM
    Comment on T-Top's post
    Other times it'll cycle the 45 minutes, go 45 more, then maybe a defrost, 45 min more running, then a 45 min cycle of nothing but room temp air. The system is set to auto fan and the fan on the unit is on so something is wrong. Tech found nothing
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #8

    Jan 28, 2011, 07:09 PM
    The defrost board will not shut off the compressor it shuts off the condenser fan motor. The compressor may be shuting off from over heating or a bad run capacitor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane XL 1200 Defrost cycle failure [ 2 Answers ]

I have a Trane XL 1200 Model TWX030C100A0 ser. # HO4202122 that has been a superb unit but now fails to initiate the defrost cycle. I can cause the unit to defrost by putting it into the AC mode when it frosts up. The defrost board is 21C140501G07 (WW28X0329). I have not replaced this board in...

Trane Heatpump AC Thermostat Wiring [ 3 Answers ]

Hello I'm trying to connect a Trane Weathetron Heat Pump (Model TWX724A100A1) To a Honeywell RTH 7400D Programmable Thermostat. This is a new installation, so there is no previous installation to observe the wiring from. Currently, the wires that we have from the outside unit are as...

Quote on New 4ton Trane or Carrier AC/Heatpump [ 1 Answers ]

I am in Myrtle Beach, South Carolina. I just received a quote of 16k to install a 4ton system. I believe this is a bit high. Does anyone have any suggestions? Thank you.

Trane xe 1200 heatpump [ 2 Answers ]

The capacitor in my heatpump went out and I found three more in my attic they have the same numbers but th mfd # is different. If I replace with a diff MFD # will it ruin my unit

Trane Heatpump defrost problems [ 1 Answers ]

Trane split system heatpunp, outside unit model AWX030C10040, S/N G07297149, MANFACTURE DATE 2/92. Defrost board 21C140501G07, WW28X0329. OUTSIDE FAN MOTOR DOES NOT RUN (WILL RUN IF YOU BYPASS THE DEFROST RELAY ON THE DEFROST BOARD.) Compressor runs but stays in the defrost mode all the time....


View more questions Search