    Ground for hot water heater
    Just replaced 2 yr old heater (warranty applied).. its a bradford white. Plumber gone by now and wanted to ask about grounding for heater... info on how to would be helpful
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jan 27, 2011, 02:22 PM

    Assuming an electric water heater. The water heater should be wired with a 10/2 with ground cable. In the circuit breaker panel the black and white should be wired to a 30 amp double breaker and the ground wire should be wired to the neutral/ground buss bar.

    At the heater the black and white should be connected to the two water heater leads. The ground should be under the green ground screw, attaching it to the frame of the heater.

    What's your question.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Jan 27, 2011, 03:50 PM

    So this is electric, right? What causes you to think it isn't grounded, its working correctly, right?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Jan 27, 2011, 05:37 PM

    As mentioned by Hkstroud, a water heater can be grounded via a 10/2 romex cable with ground. Here, the wire acts as the ground back to the ground bar at the electric panel.

    An electric water heater can also be grounded via an EMT (electrical metal tubing) or a BX cable... see images. Here, the metal tubing acts as the ground as long as it is continuous back to the electrical panel... no ground wire involved.

    As Ballenger and Harold asked, exactly what is your concern?

    Let us know more, OK?

    Mark
    Attached Images
       
    grandmeme's Avatar
    grandmeme Posts: 3, Reputation: 1
    New Member
     
    #5

    Jan 29, 2011, 01:34 PM
    Follow up on grounding water heater. Was told that unless properly grounded anode rod would rust quickly. Heater was 2 yrs old and rust a problem within a yr. emptying the tank did no good. I have to rely on the plumbers who give advice and ea. said to be sure and check 'grounding'... I watched him re-attach electricl and it looks like 10/2 romex. From one who knows -0- of electrical, I want to be sure I don't lose this tank too
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Jan 29, 2011, 01:45 PM

    What color is the wire? If orange, then that should be 10/2 with ground. If you look extremely close at the wire, it should also say what it is. Check the wire and get back to us...
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    Jan 29, 2011, 03:20 PM

    Right next to the place where where the wire goes into the water heater there should be a cover plate, held in place with one screw. Remove that plate and you should see a bare wire connected to the frame with a green screws. Printed or embossed on the cable you should see "10-2/ ground", or "10-2/with ground".

    Should not be necessary to turn of breaker, all except ground wire is insulated and quite safe.

    Please also note that if you have copper pipe the heater will be grounded through the piping.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #8

    Jan 29, 2011, 04:14 PM

    "was told that unless properly grounded anode rod would rust" you were told wrong. The anode is a sacrificial anode made to be dissolved, it can not rust , its aluminium or magnesium.
    grandmeme's Avatar
    grandmeme Posts: 3, Reputation: 1
    New Member
     
    #9

    Jan 30, 2011, 07:21 AM
    THANK YOU all so much... son due by today and will have him double check both wiring and your comments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New hot water heater installed, but no hot water pressure. Plenty of cold water? [ 11 Answers ]

Hi, I own a small plumbing service and have a problem I've never encountered before. I installed a new top vented gas water heater for a customer. Turned the main back on, bled air out of the lines, etc. Problem is there is no hot water pressure throughout the house. Cold water pressure is fine....

No water in hot or cold bathroom sink after flushing my gas hot water heater [ 5 Answers ]

Thank you. I flushed my hot water heater last night. I only turned the cold water intake to the heater off and on BUT now, after the flush, my second floor bathroom sink faucets (both hot and cold) don't work at all. The shower and the tub in the bathroom work but NOT the sink- HELP! Thanks so...

Why would, hot water only, stop flowing from (gas) tankless hot water heater? [ 1 Answers ]

Cold water flows fine. Just the hot water has stopped running.

I have very low hot water pressure from my hot water heafrom an electric water heater [ 0 Answers ]

I have very low water pressure from my hot water heater. I can't find anything wrong.. any ideas?

No hot water in shower and water heater affects both cold and hot water flow [ 1 Answers ]

1. No hot water coming from shower even though there is hot water coming from face basin in same bathroom and throughout the house( moen plumbing) 2. when water heater valve to house is turned off the cold water and hot water from shower does not flow, yet in other faucets throughout the house...


View more questions Search