    Can 14/2 wire be used for basement wiring, including 3 way switches?
    I am wiring my basement and have a spool of 14/2 as I was told this will suffice. Will it be fine for 3 way switches, recessed lighting on dimmers, etc.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jan 22, 2011, 06:33 PM
    Who "told you it will suffice"? Did they do a load determination to see what you need? Are you planning to run this for outlets too or just lighting. You might have a electric heater that will take all of the capacity on 1 line. It will not work on 3 way switches, you need 3 conductor i.e. 14/3 or 12/3. Tell us what you want to run.
    Jaymeli5's Avatar
    Jaymeli5 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 22, 2011, 06:41 PM
    I am using it for outlets as well. One breaker will have one light and one outlet. One with one light and 3 outlets. One with two Bathroom lights, and 1 GFCI. One with 3 lights on a 3way switch. One will be with 5 outlets. Entertainment room will have recessed pod lights (8) in groups of 4 on two dimmers.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jan 22, 2011, 06:48 PM

    14/2 cable is listed for 15 amps. 15 amp circuits are used for general lighting and general receptacle loads. It does not matter whether they are in the basement or elsewhere in the home.

    As Ma0641 is telling you, we really need to know what type of circuit you are designing. For example if you are using a light controlled by two switches, 14/2 will not work. It would have to be 14/3.

    However, if you are using a multi outlet circuit you are limited to 12 amps. For example, a double receptacle would be considered a multi outlet circuit.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jan 22, 2011, 07:00 PM

    You CANNOT use it for the bathroom GFI. That must be on a 20A circuit which requires #12 wire.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jan 23, 2011, 06:22 AM
    In addition to the sound advice you have received already, keep in mind, all the basement outlets, lighting and receptacles, need to be Arc Fault protected, there needs to be at least one hard wired smoke detector in the finished basement common area, and one in any room that will be a bedroom, all interconnected together and with any other smoke detectors that should be existing in the home.

    Stan has already informed you that the bathroom must have a 20 amp circuit on #12 wire, which can serve the lighting, exhaust fan and at least one GFI receptacle in that one bathroom only.

    As you, and any other reader can see, wiring a basement is much more than slinging #14-2 cable everywhere.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Typical bathroom wiring diagram including submersible sewage pump [ 3 Answers ]

Can the bathroom sewage pump be included in the dedicated 20 amp circuit for the bathroom wiring?

Wiring three switches for three lights. One red wire. [ 9 Answers ]

Here is the situation... I have one outdoor fixture, an outdoor outlet (used to be a lamp post) and an indoor light fixture. This is what I was able to get to work (turn each on an off individually without affecting anything else): All three white wires are wire nutted together. All three...

Wiring a receptacle to a three wire and two switches [ 9 Answers ]

Hello, I have two switches, three wire coming into the box is red black and white. Switch 1 is connected to the red and is connected to the other switch 2 with a small white wire. Switch 2 is connected to the white wire coming in and the black wire. I want to install a receptacle that runs all...

Wiring a basement with switches and recessed lighting [ 6 Answers ]

Hi I am wiring my basement for first time with "guidance" of an "electrician" Ive used 14/2 wiring I am installing a total of 10 recessed lighting in 2 zones, 5 in each. And 10 wall switches , 5 in each zone as well This is how I have started Run 1 14/2 wire from panel to shortest run for each...


View more questions Search