    Installing a combo meter main panel
    I'm installing a Homeline combo meter main panel and have concerns about my circuits entering the house. I see no good way to install watertight fitting between the panel and inside wall. Any ideas what is acceptable by code? I'd like to use a PVC MA.
    Thanks
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jan 22, 2011, 08:36 AM

    If you are not experienced working with electricity than please contact an electrician.

    Working with live service lines can leave you dead.
    nosnan's Avatar
    nosnan Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 22, 2011, 08:48 AM
    Great advice! I agree.

    However, I am experienced, but on commercial/industrial, not residential. I'll admit, it's been about 5 years since I've been in the field. Also, there is no 'service', this is the main panel/meter that I'm installing on new construction. I have a permit.

    I'm just not quite sure of the best method of 'watertighting' the fitting between the panel (out the back) and the dwelling.

    Thanks for the help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 23, 2011, 05:45 AM
    I assume you mean to keep the panel watertight, and not the holes into the building.

    The panel you have should be rated NEMA 3 R, or Rain Tight. The knockouts on the back of the panel are all near the bottom, I believe. These raceway entries do not need to be watertight.

    Any water that will collect in the panel will be at the bottom of the panel, and not above near the live parts. The panel will have weep holes in the bottom to allow any collected water to drain.

    If you want to water tight the hole into the building, best you can do is drill a hole slightly pitched to the outside to allow water to only drain to the exterior, and caulk around the raceway.

    PVC conduit and fittings will be fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub panel load size from main panel 200 amp to 100sub 350 ft [ 1 Answers ]

Wire conduit size fromm a main 200 amp panel to a 100 amp sub panel 350 ft away

Installing a ne Main Panel [ 11 Answers ]

I am changing the location of the meter and I decided to install a new main panel and rewire the existing one as a sub-panel keeping all the existing brakes at their place I am going to use an SER 600V cable to connect the 2 panels. My question is: How am I going to connect the SER cable at the...

Changing meter main to sub-panel [ 1 Answers ]

I'm installing a 200 amp dual meter main. Can the old 100 amp meter main be turned into a sub-panel?

Torque Specs for Installing 400A Lugs in Meter Main [ 3 Answers ]

In reading through some of the posts I see various mentions of making sure to properly torque the set screws for the lugs on the main breakers and other items. My question is, how do you know the proper torque specs and or where are they obtained? I have a Milbank M400-APS Meter Main with two...


View more questions Search