    100 amp sub panel
    In putting in a 100 amp sub panel using 6/3 wire I have wired it to sub panel but an woundering about the main do I have to put both the ground and the neutral on the same bus? Or make an
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jan 19, 2011, 06:49 PM
    Your sentence is incomplete so we don't know what you are asking after... or make an? What is the AMP rating of the main box? 6/3 is only rated for 50 Amps, not 100

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

100 amp sub panel from 200 amp main panel [ 2 Answers ]

We have a 200 amp main panel. We added another floor and decided to add a new sub panel of 100 amps. Is this OK? Should the wire gage be different from 100 maps? Your help is appreciated.

100 amp panel to new 200 amp panel and sub panel [ 3 Answers ]

I have a very small (1000sq feet) 1920 home in Northern New Jersey which 15 years ago was upgraded to breakers with a 100 amp panel. The whole house does have copper romex in it now, and I am adding a substantial addition (3000 sq feet) to the house and I want to put a sub panel in the new portion....


View more questions Search