    Three-phase System
    I can't seems to get the right answer and I totally don't know how to do it. Please someone help me.

    In Figure Q1.2, a three-phase four-wire system operating with a line voltage of 480 V is supplying a balanced motor load at 560 kVA and 0.86 power factor (pf) lagging. The motor load is connected to the three main lines marked a, b, and c. In addition, incandescent lamps (with unity pf) are connected as follows: 48 kW from line a to the neutral, 25 kW from line b to the neutral, and 14 kW from line c to the neutral. The three-wattmeter method is used to measure the power absorbed by the load in each line.
    (I) Calculate the wattmeter readings.
    (ii) Find the current in the neutral line.

    This is the figure:
    http://i486.photobucket.com/albums/rr230/Azwaney/figure.jpg
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 14, 2011, 09:39 AM
    First you convert the motor kVA to kW.

    Can you do that?
    Newton1Law's Avatar
    Newton1Law Posts: 60, Reputation: 5
    Junior Member
     
    #3

    Jan 16, 2011, 01:54 PM

    Since the load presentred by the motor is given as 560 kVA at 0.86 power factor, to get the kW drawn by the motor, it is calculated as follows: 560 kVA * 0.86 = 481.6 kW. Divde this by 3 to get the kW supplied by each phase which equals 160.5 kW. To get the kW loading for each phase then add the kW loads on each phase to get, a = 208.5 kW, b=185.5 kW, c=174.5 kW.

    Last the neutral current is found by adding the vector currents from each phase to get the resultant. At first this looks a bit complicated due to the power factor of the motor load, however, the motor load is balanced and thus it will have zero neutral current addition. This leaves only the resistive loads at unity power factor, thus the phase angle between each current will be 120 degrees if we assume zero impedance from the source and zero impedance for the wires supplying the load. Then we can find each current by dividing the single phase loads by 277 volts to get, a = 173 amps at 0 degrees, b=90 amps at 240 degrees and c = 51 at 120 degrees. Perform the vector sum of these currents to get a=173+j0 amps, b=-45-j78 amps, c=-25+j44 amps. Add these to get the neutral current of 103-j34 amps. Convert to polar notation to get 108 amps @-18 degrees. Hope this helps,
    Newton1Law

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why 3-phase is used in power system? [ 0 Answers ]

While as the single phase and two phase do not use?

Why we use three phase system not six phase system? [ 1 Answers ]

Just a quick question.

Single phase vs. 3 phase power - what makes 3 phase more efficient? [ 1 Answers ]

Hi, What is it that makes 3 phase power more efficient? Suppose I need an air compressor for a printing shop and I can choose between a 7.5HP single phase and a 7.5HP 3 phase. Ignoring that the cost of the motor is a little less for 3 phase, why is the motor more efficient and how does...

Is it a 3 phase 208V or 1 phase 208V system? [ 1 Answers ]

From a NEMA L6-30 3-prong connector in the lab, it measures 212V btwn two prongs and 122V btwn any of the two prongs to the third prong. Based on this info alone, is it a 3 phase 208V system or a 1 phase 208 system?

277v HO light on a 2 Phase System... Can it be done? [ 7 Answers ]

I tried to find tkrussell's previous post when he explained 1 phase, 2 phase and 3 phase - as it relates to voltage. The lights I want to install are Cooper's XF Falcon floodlights 250w MH - they say they are 277v and are "tritap 120/277/347" I remember something about 277v not being 240v? Is the...


View more questions Search