    Heating
    Our houses central heat does not come on to the set temperature. Thermostat is set at 76 but the room temperature reads 64. When it does come on it will run long enough to reach the preset temp. It will run for about 10 minutes then shut off for about 30 seconds then turn right back on. Will then run for about 15mins before shutting off. When I turn off the unit for a few minutes then turn it on again you can hear the fan click on but doesn't actually start blowing for several minutes sometimes not at all.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jan 12, 2011, 11:23 AM
    76 is a very high room temperature and your heater may be heating so long that it trips the high limit safety switch. The wait you are experiencing is the time it takes to cool down and reset the switch. Overheating the exchanger is not a good idea either. I would start at 70 and then go up a couple of degrees at a time. See if that works. You may need a new limit switch too, they get fatigued too.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier heating unit --fan won't work with heating [ 6 Answers ]

I have a carrier heating unit installed in 2000... it worked fine since then but now... fan will work if we turn it ON by itself... but if we turn on auto heat then heater goes on (blower like sound) but fan doesn't force the air into the house... if we turn off the heat... fan comes on...

Cost of converting electric heating to gas heating [ 2 Answers ]

I am buying a house with electric heat. I have heard it can be a lot more expensive than gas. What would be the cost of converting the house to gas heating and a/c?


View more questions Search