    GFCI spa cut off box for alternate use 50amp GFI for 15amp circuit
    Hi, I installed a specialty appliance on the driveway and need to supply a gfci circuit to it.

    Here is the issue: The main panel in the house is a Square D panel. I had added gfi breakers to it(2- 15amp) but later, after issues with popping breakers found a paper listing Square D, Technology Research Corp, and Vista as failing the manufacturers load(suitability) tests. The breakers that passed testing are Siemens QPF and Murray MP-GT.

    I have been trying to find a way to add a sub panel or replace the cut off box (outside) or even to find a 240v GFI outlet. The Main lug panels have different style lugs than the GFI breakers and I haven't been able to find anything that will resolve my situation.

    If I replace the outdoor cut off box with a spa box it will have GFI breakers but rated at 50 or 60 amps. Is this OK? I do have regular 15 amp breakers in the main panel feeding the circuit. Is there a spa type panel available with 15 amp GFI breakers?

    My thought is the 50 amp GFI breakers will act as fault trips and the main panel will control the circuit with the 15 amp breakers. I'm asking because I really want to get this right, if you know what I mean.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Jan 2, 2011, 08:33 PM
    First question... Did you say you are using 2 120 volt gfci to make the 240 volt circuit? If that is the case, it's a big no-no and against code and against good logic. A tandem breaker is the only way this would be acceptable... can you elaborate on "special appliance"? Can it be hardwired?
    amfuel's Avatar
    amfuel Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 2, 2011, 09:38 PM
    Comment on Missouri Bound's post
    Hi MB, This is a compressor, 240v 1ph 60hz on a 15amp circuit from the main panel. I have a fused cut off box located outside. It is all hard wired.

    Yes, I did use 2- 120v GFI breakers in the main panel.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Jan 2, 2011, 09:44 PM
    You must use the tandem breaker... period. If just one of your two breakers should trip, the motor would still be energized. And if it's hardwired, why do you require a gfci?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

In a spa installation does the GFI breaker go in the disconnect box or main panel? [ 2 Answers ]

In a spa installation does the GFI breaker go in the disconnect box or main panel?

GFI or GFCI Limit on one circuit [ 1 Answers ]

I am wiring my own garage, and have searched the Nec codes on many areas. There seems to be some confusion with a detached garage as to the number of gfi outlets, whether all need to be or just some. My question is this: How many gfi outlets, or outlets protected by the one Gfi outlet can I have...

30amp GFCI to 50amp GFCI [ 1 Answers ]

I have a square D panel box with 200 amp service coming into the house. I have a square D 30 amp double pole gfci breaker that was put in last year for a hot tub. I am now getting a new hot tub, and it requires a 50amp gfci breaker. The 30amp currently in place says type/tipo HOM. It is...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search