I'm in the process of remodelling my third floor and adding a new bathroom up there. The previous owners put in a new 4" vent stack which is currently only connected to a washer on the second floor. They had intended on putting a bathroom in themselves on the third floor but never did, and they did not bother to run the vent stack through the roof. Instead, the stack sticks up out of the floor about 5ft, and there is some kind of filter on the top of it.
The problem is, I would like to put the bathroom on the opposite side of the room, approx 16 feet away and vent it out through the roof there. I have a straight shot under the floorboards to do this.
So, essentially, I'm asking whether it is ok to run a vent stack straight up from the basement to a third floor, then run it horizontal for 16 ft (making sure it drops 1/4" per foot), and then 90 degree verticle again and through the roof.
Any assistance on answering this question would be appreciated.
Thanks in advance
|
|
 |
Senior Plumbing Expert
|
|
Dec 28, 2010, 12:19 PM
|
|
Hi Rgb71...
YUP! No problem on using the 90s, however, plumbing codes would recommend long sweep 90s, OK? Be sure to maintain that 1/4" pitch so you have no issues in the future.
Also, note here that the washing machine will need to have an 1.5" vent installed and connected to other vents upstairs at 42-48" minimum of the floor.
If codes allow, you might also install a mechanical vent (called an AAV), but most cities/towns won't allow them. No matter what, you need to add the vent to the washing machine or the PTRAP will get siphoned out as the large volume of water from upstairs rushes by to the basement sewer and sewer gasses will escape from the washer drain... ;)
More questions? Let me know...
Mark
|
|
 |
New Member
|
|
Dec 29, 2010, 04:01 PM
|
|
Comment on massplumber2008's post
Hi Mark,
Thanks for the quick response. Much appreciated!
|
|
 |
Senior Plumbing Expert
|
|
Dec 29, 2010, 05:55 PM
|
|
Glad to help. Pop back if you need any help on the venting, OK?
Mark
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Old stack vent system vent tub
[ 8 Answers ]
I wrote in another thread about my slow draining tub.
The consensus is that I need a vent, preferably downstream from the sink ( many mentioned an AAV just beyond the trap) now my issue is that I have a pedestal sink, and the plumbing is not really accessible around the sink to put in any kind...
No vent stack - possible?
[ 4 Answers ]
We've been living in a house for 3 years and have been doing some remodeling throughout. It appears that there is no venting system in the house. There are 3 toilets, 4 sinks, and 2 showers, however we cannot find a vent stack anywhere. My roofer noticed this when he took off the old roof - he...
Is It Vent stack?
[ 3 Answers ]
Hi, Around late December my kitchen sink started to drain real slow, so I got a snake and snaked out he lines. Pulled back the usual "black goo" and everything seemed to be fine. Then this weekend I doing A little yard work and notice water coming out from behind the siding. Upon further...
Vent stack
[ 1 Answers ]
Hi, I think we have a leak in the main stack,there is water at the bottom of it and it smells like toilet water. Can this be fixed or do I have to have a new one installed, and is it expensive
No vent stack?
[ 3 Answers ]
I recently purchased an old house and the toilet drains slow and bubbles. I cannot locate any plumbing venting at all. The plumbing is all located within 4 ft of the main drain going out through the basement wall, with the kitchen sink, bath sink, tub all connecting to the toilet line then out...
View more questions
Search
|