    200 amp service to 125 subpanel detail help
    I am running 4/0-4/0-2/0-2 mobile home feeder cable 220 feet from a 200 amp meter to a 200 amp Exterior load center (Main Breaker). I will then connect to a 125 amp subpanel inside my cabin fed from a 125 amp breaker. Here are my questions:

    1) Can I use 2" Sch 40 PVC for this service cable?
    2) What size cable should I use from outside 125A breaker into the interior load center lug. Distance is about 15 feet, but the 4/0 is to big to connect to the 125 service panel lugs.
    3) Do I connect the #2 green ground cable on the mobile home feeder to the Neutral in the Meter socket, run it to a rod or don't use it at all and ground the main breaker?

    Thanks for any help!
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 29, 2010, 04:13 PM
    How about a little more detail?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Nov 29, 2010, 07:44 PM

    #1 depends... what is "type" of wire the feeder cable is? (letter designatiopn) For example, THHN would be OK, while RHW would require 2 1/2".
    #2 A 125 amp circuit would require a #2 copper wire.
    #3 The ground and neutral can oly be together at the first service connection. This is usually where the first disconnect is located, usually in the main panel. After that, all subs must have the groud bus isolated from the neutral, and a grounding rod must be used.
    Does this help?
    br549scooter's Avatar
    br549scooter Posts: 5, Reputation: 1
    New Member
     
    #4

    Nov 30, 2010, 08:46 AM
    Comment on Missouri Bound's post
    Thanks for the help, but am still confused about the ground wire (RHW - Aluminum 4 wire) that is with the 2 Conductors and Neutral. Where do I connect this ground cable at the Meter socket? Do I connect it with the neutral or to an earth ground rod?
    br549scooter's Avatar
    br549scooter Posts: 5, Reputation: 1
    New Member
     
    #5

    Nov 30, 2010, 09:27 AM
    Comment on Missouri Bound's post
    My main disconnect is at the cabin (220' feet downstream). Would it be better to add a main breaker at the pole with the meter and ground it to a rod there? This is the only way I can make sense of the ground cable that is included w/ feeder cable.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service Panel Issues/replacement 125 AMP to 200 AMP [ 7 Answers ]

Hello, I recently started a remodel in my basement (total home with basement = +/- 1900 sq ft) and have consulted with a few electricians and have had a number of different issues and bits of advice which have left me confused. My house was built in the 40's and has had many electrical...

125 amp service panel tapped from the line side of my 200 amp service panel. [ 1 Answers ]

I have a 125 amp service panel for my basement, being fed from the line side of my 200 amp service panel. Is this legal? Does the 10 foot tap rule apply here?

Wiring my barn using a 125 amp subpanel. [ 5 Answers ]

I have a 200 amp feed through panel about 40 feet from my barn. The 200 amp feed through main panel feeds my house. The house uses a 100 amp main. I want to install a 125 amp sub panel in the barn and put the main breaker in the feed through panel. Can I do this without having a main...

Service upgrade: Is 200 Amp necessary? Or will 125 Amp work? [ 1 Answers ]

Hi, I recently bought a 1950s home with 60 Amp service. We are planning the upgrade now and after getting several estimates, it appears that there is a difference of approx. $1200 by the way getting 125 Amp or 200 Amp (it's $3200 vs. $4400, with the local utility company being responsible for...


View more questions Search