    smithnort's Avatar
    smithnort Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 7, 2007, 02:23 PM
    Furnace kaaput!
    This morning I awoke to find the furnace not working the thermostat was calling for heat the inducer motor would kick in then I would hear the pilot clicking on but it would not light the furnace. The last two years I have had to change the intermittent pilot module I changed this again but it did not solve the problem this time. Looking for aN answer in N.Y.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Jan 7, 2007, 09:42 PM
    Most of the time when your module is making the pilot lighter click there is a problem in the pilot itself. Either the spark is not sparking where the pilot gas is or the pilot is dirty and not getting enough gas through to light the way it should. Next time you try to get your furnace to run and you hear the clicking noise try to light the pilot with a match. Good luck
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #3

    Jan 8, 2007, 04:15 PM
    Look for 24 volts at the gas valve MV/PV to PV terminals, does it have 24 volts there?
    Brand, Age and efficiency, if you know.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a furnace thermostat to manually operate the furnace fan [ 2 Answers ]

I have two wires connected to my furnace thermostat. There is a place labeled G on the thermostat. Can I simply run a wire from the G terminal on my thermostat to the terminal labeled G on my furnace fan relay to operate the fan separately?

My intertherm furnace pilot lights but furnace won't kick on [ 5 Answers ]

I need some diagnostic help. We have a full propane tank. A new burner plate (last year) and the blower works. We light the pilot but the knob should pop up after one minute thus lighting the furnace. It won't pop up. What part should we replace? The furnace is a 17 year old Intertherm MGH...

My furnace [ 1 Answers ]

Why does my furnace blow cold air instead of hot air?

Comfortmaker Furnace Fan blows in line fuse and will not allow furnace to work [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can...

New furnace [ 9 Answers ]

I have got an old furnace I am going to have to replace eventually. I was looking for general advice right now what I should know when finding someone to replace it. I don't want to get into a situation where it will cost me thousands of dollars when I don't need to. I have a gas furnace with hot...


View more questions Search