    Tandem Breaker Allowed?
    Is it okay to use a tandem breaker in this service panel? It is supplying a 100-amp apartment.

    1-20 amp Bath
    2-20 amp small appliance circuit 1
    3-20 amp small appliance circuit 2
    4-15 amp Lights/Receps
    5-20 amp lights/receps

    Circuit 5 will be upgraded to an AFCI breaker if that matters.
    Attached Images
     
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 3, 2007, 06:57 AM
    Sure, no problem adding a tandem breaker to this panel, I believe this panel can handle six tandem breakers.

    However, may I list a few observations of other problems/violations I see?

    The Main Breaker is clearly a 100 Amp breaker, and the incoming wires, and the subfeed wires off the subfeed lugs do not appear to be 100 Amp rated.

    The Main incoming wires are only clamped by the connector, and are not in any raceway(conduit).

    Main neutral is not combined with the incoming hot wires.( Must be combined to prevent induction heating effect caused by the magnetic flux of AC current.)

    The top and right connectors appear to be for Service Entrance Conductors, (The top must be if they are feeding a Main breaker) and even thou one has a bonding bushing, neither are bonded correctly.

    The Neutral lug on the right has two wires in a lug only rated for one wire.

    Since the Main breaker is in this panel, the Neutral bar should be bonded to metal box, I do not see a Main Bonding screw or jumper.

    The Romex cable at bottom left is missing a connector.

    The MC cable at the bottom right is missing an Anti-Short Bushing (AKA Redhead).

    The bit of utility meter I see at the bottom tells me that his building is a multi-family dwelling (apartment), should check to determine if non-licensed or permits are not required in that town, city, county, state.

    Clearly, by the violations I found in one picture, tells me that a un-qualified person did that work.
    Ohio_Remodeler's Avatar
    Ohio_Remodeler Posts: 85, Reputation: 1
    Junior Member
     
    #3

    Jan 3, 2007, 09:40 PM
    Thanks for the feedback. The last owner/maintenance person clearly did not wire this properly. As it is a multi-family I am not doing the wiring myself. I am in the process of determining exactly what needs to be done and will then hired a licensed electrician.

    Could you tell me what gauge the main wires are and what gauge would be rated for 100 amps?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 4, 2007, 02:56 AM
    #3 THHN copper or #2 XHHW aluminum
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jan 4, 2007, 04:34 PM
    Sorry I misread your last question:


    Quote Originally Posted by Ohio_Remodeler
    Could you tell me what gauge the main wires are and what gauge would be rated for 100 amps?

    When I gave #3 copper and # 2 aluminum, I meant these are the 100 amp rated wires.

    The existing wires appear to be #6.
    dei2007's Avatar
    dei2007 Posts: 12, Reputation: 1
    New Member
     
    #6

    Jan 4, 2007, 08:04 PM
    Quote Originally Posted by Ohio_Remodeler
    Is it okay to use a tandem breaker in this service panel? It is supplying a 100-amp apartment.

    1-20 amp Bath
    2-20 amp small appliance circuit 1
    3-20 amp small appliance circuit 2
    4-15 amp Lights/Receps
    5-20 amp lights/receps

    Circuit 5 will be upgraded to an AFCI breaker if that matters.
    That panel is against the NEC.If that is a subpanel you will have to take those grounds off the neutral bare and put a ground bar in mounted straight the inside of the panel.Yes tandems are OK
    Ohio_Remodeler's Avatar
    Ohio_Remodeler Posts: 85, Reputation: 1
    Junior Member
     
    #7

    Jan 5, 2007, 03:36 AM
    Why is this panel against the NEC? It is not a subpanel it is a service panel for an apartment. Assuming the violations that tkrussell mentioned are taken care of it still will not comply with the NEC?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jan 5, 2007, 03:57 AM
    As far as I am concerned it is fine to use. I am not sure what dei2007 means by "That panel is against the NEC.", besides what I have mentioned.

    Oh, one thing I omitted from my list, the Main breaker will need a Retaining kit, your electrician should know what I mean and why.
    dei2007's Avatar
    dei2007 Posts: 12, Reputation: 1
    New Member
     
    #9

    Jan 5, 2007, 05:54 AM
    Quote Originally Posted by Ohio_Remodeler
    Why is this panel against the NEC? It is not a subpanel it is a service panel for an apartment. Assuming the violations that tkrussell mentioned are taken care of it still will not comply with the NEC?
    You probably have a main panel outside where all your 240 volt stuff is fed from.Then your inside panel is considered a subpanel, then in return your grounds have to be separated from the neutral bar.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Jan 5, 2007, 06:25 AM
    Die if you look close below the panel, there is meter for another apartment, and Ohio admits this is a multifamily dwelling, and there is a breaker labeled 'MAIN", therefore this is not a subpanel, which if it was, you are exactly correct about separating grounds from neutral, but this appears to be not applicable.

    Very seldom is there a Main Switch upstream of metering such as this type and age.

    Otherwise, I would have mentioned it.

    And what concerned Ohio is your statement that the panel itself was not code compliant.

    The best thing he said was he will be having an electrician make any necessary repairs or changes.

    The bset method of offering advice is to only offer defintite advice about a condition that is definite, otherwise, offer advice conditional on a possibility of a condition.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is Romex allowed over concrete block? [ 2 Answers ]

I have a detached building with a block foundation. On the inside, the top of the blocks is about 4" above the concrete floor. The walls are aligned with the outside of the 8" wide block therefore there is a 4" wide shelf (top of the blocks) that runs along the perimeter of the building. I used...

Am I allowed half of his tax return? [ 2 Answers ]

My spouse and I have been separated for 3 months. I recently filed his tax return online for him, at his request, and he wanted it direct deposited into my account. He told me he would give me 600.00 of it, although he is getting 1800.00 back. Due to some very violent behavior a couple of days...

Why is this allowed? [ 7 Answers ]

There are reports that once the rescue of people is done, the National Guard has orders to shoot any stray animal on site. Animals are starving. They swim to rescue boats and are being turned away because the boats are for people, yet the rescuers for animals are not allowed to rescue them. ...

Is an "S" trap ever allowed? [ 4 Answers ]

The house we've just moved into has the piping for a full bathroom in the basement floor complete with an ejector pump. My intention is to put a washer\dryer and laundry sink in that area of the basement instead of a bathroom. There are 4 drain pipes running up from the floor. Three of the...

Error Message - Column Not Allowed Here [ 3 Answers ]

I tried to create a table and got the following message: COLUMN NOT ALLOWED HERE. What is the solution for this? Regards MATHEW


View more questions Search