    What Size Wire would I have to run for a 80' run running 22amps and 2052watts constatly
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 18, 2010, 01:26 PM

    Okay,

    One of us is on the wrong page.

    Simple Ohms Law calculations provide a voltage of 93.XX volts.

    So basically, you want to use 94 V across an 80 ft' conductor to a 2050 Watt load. Is this correct?

    Since you did not give a lot of information, I used UF-Copper @ 60C and suggest #8/2 Copper. With a #8 Ground. Also you would need a 30 Amp Single Pole Breaker.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Oct 18, 2010, 01:47 PM

    Don, I seriously doubt he is using 94 volts. I simply think he is not sure what he is talking about.

    Vincent, please describe a little clearer what it is you are doing.
    What do you mean by 22A and 2052 watts? This is very confusing.

    Where will this wire be run?
    What is the load you are connecting?
    What is the voltage?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Oct 18, 2010, 03:40 PM

    Vincent, what the guys are saying is volts X amps = Watts Unless you are using some kind of transformer one of your numbers is off. Where are you located and what eqipment is drawing the load?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 19, 2010, 04:47 AM
    Even though Vincent gave odd numbers for amps and watts, need to know the voltage to perform the proper voltage drop calculations.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Oct 19, 2010, 05:09 AM

    I agree and that was what I was trying to show.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire? [ 5 Answers ]

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire coming from a 200amp. Service? Any info. Would be appreciated. Regards, Garry

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...


View more questions Search