    My heat turns off but fan keeps going?
    My heat reaches set temperature and turns off, but the fan keeps running... does anybody know what's the problem?? I can't turn fan off...
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Oct 16, 2010, 12:22 PM
    The fan should run after the flame goes out. This is to extract all the heat from the exchanger. If the fan runs for more than 1-2 minutes and won't shut off, your limit switch may be bad, not that uncommon. Take off the front of the heater and above the burner area you should see a box. Some have 1 dial, some 2. The 2 dials may be marked fan on and fan off. The 1 dial has fan off on the left side and fan on on the right side. Fan on sets at 125-130 and off at 95-100. Sometimes the contacts get a bit dirty. Use a screwdriver to spin the fan off switch back and forth, or slide it forward and back, set it at 95 and then run it through a cycle. If it still doesn't work you probably need a new fan switch. They are usually easy to replace. Draw a wiring diagram, mark the wires, take out the screws holding the unit in place, replace with a new unit and connect the wires. Should take 20 minutes or so. Good luck!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

My ac fan turns off when I switch it to ac from heat [ 8 Answers ]

Myblower motor in the house the one that blows air thruthe vents shuts off when I turn the thermostat to ac but as soon as I change the thermostate to heat the blower turns on like nothing is wrong

Fan turns off, no heat [ 9 Answers ]

My furnace does not seem to be blowing air. At first I thought it was access panel switch due to a bent panel. However, I held it down while someone else stayed by a register to check airflow and there was very little if none. Also, the gas never lit, but I could smell some. Thoughts?

Light turns on & Fan turns off automatically when a remot is installed [ 2 Answers ]

I bought a Hunter remote separately and installed to my ceiling fan. Everything works good except the following problem. I turn on the fan & turn off the light before I go to sleep and in the middle of night the light goes on and fan turns off. This happens a few times until morning when I turn...

Furnace turns off heat and fan continues blowing cold air. [ 14 Answers ]

Carrier split unit Model 58RAV055-GC Circuit Board at Furnace CES0110057-00 Natural Gas I am experiencing a problem with my heat. I have a programmable zones thermostat and noticed that the air was not coming out hot when it was suppouse to be. The temperature was set to 75 but the temperature...


View more questions Search