    Electrical-finishing basement
    OK, I don't know much about electrical, but I'm trying to finish my basement and this is what I have so far. I have a 50 amp break in the main box feeding a subpanel in the basement which has two 20 amp breakers. One feeding about 8 outlets and 1 feeding another 8 outlets. I'm using 12/2 wire for this so far. My question is this the proper setup so far? Also, I'm about to start on the lighting and planned on putting all the lights on one breaker? Would this be OK and would I still use 12/2 wire? Thanks
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Sep 27, 2010, 07:18 PM

    Wire size is tied to breaker size. If you have a 20 amp circuit you stay with 12/2 wire. It is not only Ok it is a MUST. If your dropped to 14/2 you'd have wire that is rated for 15 amps but on a 20 amp breaker, no protection there. The number of outlets on a breaker is not much of a concern but the things plugged into those outlet is a concern. What else will be plugged into the same circuit as the lights? If any of these things trips the breaker you'll be in the dark.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Sep 28, 2010, 04:22 PM
    It all depends on what you will be plugging into the outlets. If you put a space heater@1500 watts and a toaster oven @1500 watts and then a TV. You will be overloaded on any 8 circuit run. Make sure to spread the load around. I would put the lights on at least 2 breakers. That way you are not in total darkness if the breaker trips. Many electricians will run 12 AWG to a junction box using a 15 Amp breaker and then run 14AWG for lights. Unless you are going to really load the lighting, 14 AWG if fine. How many spaces in the subpanel and who installed it? Subpanels are treated differently when it comes to the neutral. It is isolated from the subpanel and wired back to the main panel.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Sep 28, 2010, 04:46 PM

    Lets keep in mind you can not mix 12/2 and 14/2 wire on a 20 amp circuit. OP states he has two 20 amp breakers so no 14/2 anuwhere is allowed. http://www.cerrowire.com/default.aspx?id=46
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Sep 29, 2010, 07:21 AM

    Gentle reminder, if you are in an area that has adopted the 2008 NEC codes, that you will need to use tamper proof receptacles and Arc Fault breakers for a new installation.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Sep 29, 2010, 04:02 PM
    Comment on ballengerb1's post
    I suggested a 12AWG with a 15 amp breaker, not a 20, for a home run, then go to 14. I would hope he is adding new circuits for the lighting.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #7

    Sep 29, 2010, 04:33 PM

    I am just trying to stick with what he has in place and what his actual question was. He already has two 20 amp breakers and circuits in place. I would like to see lights and outlets on separate circiuts but he should not think he can bring in 14 gauge wire or cable into this setup.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Finishing my basement [ 2 Answers ]

I know it will vary according to the types of materials used but I am looking to finish my basement in to one large bedroom, a smaller bedroom, a small full bath and a living room/ kitchenette. Kind of like a mother-in-law suite. Can you tell me approximately how much that will cost?

Finishing a basement / electrical sub-panel wiring [ 2 Answers ]

From a main 200 amp house electrical panel what kind of wire do I need to put in two remote sub-panels for a 100 amp service and a 50 amp service. Also, without tearing out walls to string new wire, can I use some existing wire runs that are not being used that have the following markings:...

Basement Finishing Electrical [ 3 Answers ]

We are finishing a 1600SF basement... 200A Service Panel with 12 open slots... I want to run 14-2 and 14-3 for the entire project... 15A circuits with no more than 8 outlets or 6 recessed lights with 65W floods on any one breaker... Also have a bathroom with a shower going in... In the...

Finishing my Basement [ 3 Answers ]

How much will it cost me to finish my basement? It is 1890 sf

Finishing Basement Electrical [ 3 Answers ]

Hello. Great site! I have been working on a plan to finish my basement and I would like to run the electrical plans by you and ask some questions. This will be a little long, sorry. First a little background. I am Electrical Engineer, but deal mostly with small electronics. I am going to submit...


View more questions Search